 REALLY small PTO generator

I've got a JD 4110 gear on order, and had a transfer switch installed when we added a garage, but no generator as yet. We lose power up on this Vermont hillside 4-5x a year, and have been without power the past 2 days, so my attention is on this problem!

My calculations show I'd need about 8KW peak if I was running everything in the house. When I laid out the transfer box, I was pretty careful to distribute the motors on different legs and different circuits, so I think that 8KW is very conservative -- obviously I don't need to run everything at once.

I'm wondering if anyone makes a PTO generator smaller than the 10k units JD sells (which seem to be the same as the much cheaper one in the Northern Tools catalog). Or is the 10K unit (which requires 24hp PTO to reach 10k) fine on the 4110 (17hp PTO) if I don't try to max out the wattage?






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 10-17-2003, 10:46 Post: 66424
Murf



View my Photos

View my Photos  Pics
Join Date: Dec 1999
Location: Toronto Area, Ontario, Canada
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 7054
 REALLY small PTO generator

The horsepower requirement really only factors in when you get to, or near, full rated output on the genset.

I have run really big gensets with much less power than called for with no problem, as long as you are running much less load on the genset also.

Bear in mind however, HP to a 'tractor person' is like feet to a boater or an RV'er, you will always want/need/buy more.

IMHO buy the bigger 10kw. unit now, it will run just fine with a load of 5kw or 6kw on it. If you find it lugging, or pulling the rpm's down just reduce the load till it handles it OK.

Sooner or later you will get a bigger tractor, then you will be glad you bought that bigger genset way back in 2003.

Best of luck.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 10-17-2003, 11:39 Post: 66430
Art White



View my Photos

View my Photos  Pics
Join Date: Jan 2000
Location: Waterville New York
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 6854

2
Filter by User
 REALLY small PTO generator

Murf did a good job for you. The extra power to get the unit to it's full potential is there with your tractor. If you do start to overload it you will hear it on the tractor load.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 10-17-2003, 11:40 Post: 66431
Art White



View my Photos

View my Photos  Pics
Join Date: Jan 2000
Location: Waterville New York
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 6854

2
Filter by User
 REALLY small PTO generator

Murf did a good job for you. The extra power to get the unit to it's full potential is there with your tractor. If you do start to overload it you will hear it on the tractor load.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 10-17-2003, 12:00 Post: 66435
Chief



View my Photos

View my Photos  Pics
Join Date: Jul 2003
Location: Southwest MiddleTennessee
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 4284
 REALLY small PTO generator

I think Murf nailed it!






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 10-17-2003, 12:04 Post: 66437
DRankin



View my Photos

View my Photos  Pics
Join Date: Jan 2000
Location: Northern Nevada
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 5105

2
Filter by User
 REALLY small PTO generator

If you do the math, I think you may find the Deere unit is cheaper than the Northern unit.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 10-17-2003, 13:19 Post: 66443
wigglybridge

TP Contributor

View my Photos

View my Photos  Pics
Join Date: Jul 2003
Location: Vermont
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 82

3
Filter by User
 REALLY small PTO generator

Thanks to all for the followups!

Mark, how do you figure the math for the Deere being cheaper than the Northern? If that includes the Northern trailer, I was figuring on doing my own, since the Northern one is sized for a 60kw generator, and looks almost road-worthy with those tires! I was thinking of just getting a set of wheels and cutting a chunk of plywood...

Otherwise, it looks like $1000 from Northern or about 1700 from my JD dealer.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 10-17-2003, 23:16 Post: 66514
DRankin



View my Photos

View my Photos  Pics
Join Date: Jan 2000
Location: Northern Nevada
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 5105

2
Filter by User
 REALLY small PTO generator

Yes, with the trailer and shippng, at least to my location, it is a wash.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 10-18-2003, 08:03 Post: 66526
TomG

TP Contributor

Join Date: Feb 2002
Location: Upper Ottawa Valley
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 5406

2
Filter by User
 REALLY small PTO generator

Well, let's be a little careful here. The question is whether an under-powered generator setup is bomb proof and if not do you want to run a risk. I'd take a careful look at eny electric motors run, what there start up surge requirements are and what's the potential for them starting at the same time. In thinking about risks, it's good to keep in mind that people don't think the same during power failures; the generator may not always be attended and people other than yourself may turn things on and off.

The risk is that if a load lugs the engine the AC frequency falls off and power draw increases. There's a chance that the load wouldn't pop a circuit breakers nor be enough to kill the tractor engine. In that circumstance, an electric motor could burn up.

Probably not a huge potential for that happening but it might be good to think whether you want to protect yourself against any potential. Smaller main breakers or a separate disconnect would provide protection. On the other hand, a large generator reduces the chance of inadvertently running a generator for prolonged periods in its peak rather than continuous power range, and that's a plus.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 10-19-2003, 11:34 Post: 66569
wigglybridge

TP Contributor

View my Photos

View my Photos  Pics
Join Date: Jul 2003
Location: Vermont
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 82

3
Filter by User
 REALLY small PTO generator

Tom, thanks for the extra cautions. The transfer box is pretty well balanced leg-to-leg and circuit to circuit, I was careful to get the motors and other big loads distributed evenly so we could be selective.

I'm lucky to have a pretty savvy wife (in fact, I could put commas between those words. Wink yeah right SHE was the one when we visited the dealer and were looking at upscale lawn tractors that said: "I want something with a bucket"!

So in the event she ends up hooking up the generator and hitting the transfer switches when I'm not here, she'll probably be more cautious than I would and just use what she really needs.

Judging from the feedback here, I now plan to go with the 10kw unit, and figure that at the PTO hp difference, 17/24x10kw will get me to about the 7500kw area, which would almost max out my transfer box, which was sized for everything running and allowing for simultaneous motor startup. So hopefully, I'm over-engineered here, but like I said, we're pretty cautious anyway.

Thanks again to everyone and to Dennis for such a great resource!






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
Reply | Pop Up Window Reply | Add PhotoAdd Photo


Page [ 1 ] | 2 | | Next >>

Discussion Boards > Active Subjects > Messages as Posted > Generators Forum

Thread 66423 Filter by Poster:
Art White 2 | Chief 1 | DRankin 2 | Murf 1 | TomG 2 | wigglybridge 3 |

 (advanced search)

Picture of the Day
DennisCTB

Current Events - Winter Storm
Winter Storm


Unanswered Questions

Gas Generator Weather Protecti
Horse Injured Polyrope Electri
Do electric fences keep out de
Any Peruvian Paso Owners Out T
gas powered post driver
My new born foal is really sic
Trailer Axle
dump trailer blueprints


Active Subjects

Gas Generator Weather Protecti
Went to see Dennis Reis this w
Signs to look for prior to lab
leg injury
Broodmare has welts all over h
Some Christmas Humor For Horse
poles in the ground vs. concre
ever thought about moving?


Hot Topics

new app owner
Some Christmas Humor For Horse
Any Peruvian Paso Owners Out T
Heating a Garage
Gas Generator Weather Protecti
Do electric fences keep out de
gas powered post driver
Trailer Axle


Featured Suppliers

Mountain Creek Labradoodles
      MountainCreekLabradoodles.com





New Forums on Gun Sport Shooting and Hunting -- BarrelPoint.com  New Forums on Horses ManePoint.com
Talk Horses at ManePoint
Hunting + Gun Sports at BarrelPoint



Most Viewed

+ 3 Pt PTO generators
+ Generator set up ideas wanted
+ PTO Generators Observations
+ Best Portable Generator 7500W Review
+ PTO driven vs Gas engine
+ PTO Horsepower and Generator Question
+ I love my Generator
+ Features to look for in stand alone generator
+ building budget auto-backup system
+ Yamaha Generator problem

Most Discussion

+ Generator set up ideas wanted
+ PTO Generators Observations
+ 3 Pt PTO generators
+ PTO Horsepower and Generator Q
+ I love my Generator
+ Features to look for in stand
+ Yamaha Generator problem
+ Best Portable Generator 7500W
+ Power stability with PTO gener
+ Measuring Frequency in a gener

Newest Topics

+ no electric power
+ Premium Fuel for Generator Avoid Ethanol Myth
+ How to increase Portable Generator Wattage output
+ Gillette vs Winco Generator Review
+ Best Portable Generator Temporary Shelter
+ Portable Generator House Backup Grounding
+ Dielectric antioxidant grease
+ Welder generator burning up tool switches
+ Welder generator burning up tool switches
+ PowerBoss Brush versus brushless Generators
















Turbochargers for Tractors and Industrial Machines
Cab Glass for Tractors and Industrial Machines

Alternators for Tractors and Industrial Machines
Radiators for Tractors and Industrial Machines

Driveline Components for Tractors and Industrial Machines
Starter Motors for Tractors and Industrial Machines