 Yamaha Generator problem

Billy, you are right that the motor will stop if you disconnect EITHER of L1 or L2, however it is certainly not the right way to do it, nor is it safe since the 'other' leg is still 'hot' in the motor as Joel pointed out.

In some states switching a single side of 220 is not legal either. You should always use a DPDT switch and break both hots.

Best of luck.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 08-21-2007, 10:06 Post: 144872
Billy

TP Contributor

View my Photos

View my Photos  Pics
Join Date: Oct 1999
Location: Southeast Oklahoma
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 975

7
Filter by User
 Yamaha Generator problem

Murf, What Joel pointed out is very true but each of my motors have their own breaker. I would never even think about working on one unless the breaker was off.

As far as the on/off switches go, I'll try to explain one type I use. Say a feed line. On the end of the feed line there's a control pan. In this control pan there's a paddle that operates a micro switch. When the feed gets low the paddle moves down straight and activates the micro switch. All the micro switch does is open or close L1 or L2 (according to which L you chose when wiring). The fans are a little harder to explain other than they all are wired into relays and the relays are controlled by a computer. Each fan has it's own relay. The relays break either L1 or L2 which shuts that fan off.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 08-21-2007, 10:58 Post: 144876
Murf



View my Photos

View my Photos  Pics
Join Date: Dec 1999
Location: Toronto Area, Ontario, Canada
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 7054

6
Filter by User
 Yamaha Generator problem

Billy, I understand how they work, I have a similar system in the milk parlour.

IMHO though, the micro switch should trip a DPDT magnetic switch, that way you have two levels of safety, first the micro switch can be only a low voltage trigger circuit, and secondly, the system is absolutely dead unless running.

Best of luck.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 08-21-2007, 12:03 Post: 144878
Billy

TP Contributor

View my Photos

View my Photos  Pics
Join Date: Oct 1999
Location: Southeast Oklahoma
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 975

7
Filter by User
 Yamaha Generator problem

Murf, I guess one can't be too safe but it can get overly costly. The way I look at it is "if it ain't broke, don't fix it". By the way, the micro switches I use are rated at 10 Amps and 250 VAC.

Thanks for the discussion.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 08-22-2007, 15:47 Post: 144913
AnnBrush



View my Photos

View my Photos  Pics
Join Date: Mar 2004
Location: Troy OH
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 462
 Yamaha Generator problem

If you use a 110V power source and energize one leg of a 220v circuit you have not "powered half of the circuit". A 220v single phase motor requires 220V potential difference between the two lines (L1 and L2) to complete it's circuit. Powering this with the "110v setup" as described produces 0 volts between L1 and L2. The voltage between one line and neutral is irrelevant to the motor. Here we need to draw the distinction between operation and safety issues. While prudent from a safety standpoint (Line to neutral voltage), 220v devices can draw no power from a single phase 110v supply when no connection to the second line is made (no circuit completed) - if they do you have a line to neutral or line to ground fault in the 220v device.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 08-22-2007, 16:11 Post: 144916
kthompson



View my Photos

View my Photos  Pics
Join Date: Oct 2005
Location: South Carolina
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 5139

5
Filter by User
 Yamaha Generator problem

I would guess this thread has become hijacked already but something I use to see (out of that work now) which many did not pay attention to is the proper wiring of a lamp or light fixture. The "live" part is the part of the center of the buld and not the outside base of the bulb. So simple but so often given no attention to. If wired backwards it is possible to touch 110 volts with some fixtures. Much like breaking just one leg of a 220 circuit. Stay safe. kt






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 08-22-2007, 16:36 Post: 144918
candoarms



View my Photos

View my Photos  Pics
Join Date: Mar 2007
Location: North Dakota
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 1930

6
Filter by User
 Yamaha Generator problem

KThompson,

I'm not sure that I would consider this thread as being hijacked, as the conversation is relevant to all things that could cause a problem with any generator setup.

I was called to do a repair on a dental chair, which had caught on fire in a dental office. I quickly identified the problem and repaired it.

The dentist had kicked the plug and broken the wires on the cord. He removed the plug, trimmed the broken cord, and then re-installed the plug.......INCORRECTLY. POOF! Flames shot out, which burned his chair and his carpet.

On any 110vac plug, there are three wires.....black, white, and green.

Black (Hot) always goes on the gold terminal in the plug, or on the narrow male spade.

White (Neutral) always goes on the silver terminal in the plug, or on the wider male spade.

Green (Ground) is installed on the green screw in the plug, or on the round male ground connector.

Any switch that is installed in a 110vac line, such as a lamp, should be installed in the BLACK line....or the hot wire.

Any switch installed in a 220vac circuit should always break both the L1 and L2 (both hot) lines.

And a word of caution for those who run back-up generators........

Any or all of your sensitive electronic devices may be destroyed by your generator, unless your generator has a quality voltage regulator installed on it.

Some generators do not have this.

Without this voltage regulator, a sharp voltage spike from your generator will fry your television, computer and alarm clocks, as well as anything else in your home that contains digital circuitry.....such as the microwave display panel, etc.

Even a large voltage spike will not harm your blower motor on your furnace, but it could easily take out the circuit board that controls it.

When you purchase a generator, spend the extra money to get yourself a quality machine that regulates the output to a very high degree.

Joel






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 08-22-2007, 18:33 Post: 144922
Billy

TP Contributor

View my Photos

View my Photos  Pics
Join Date: Oct 1999
Location: Southeast Oklahoma
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 975

7
Filter by User
 Yamaha Generator problem

Good post Joel but when you say "Any switch installed in a 220vac circuit should always break both the L1 and L2 (both hot) lines.", what could happen if you don't?






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 08-22-2007, 18:58 Post: 144923
candoarms



View my Photos

View my Photos  Pics
Join Date: Mar 2007
Location: North Dakota
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 1930

6
Filter by User
 Yamaha Generator problem

Billy,

Nothing will happen......until somebody attempts to work on the motor, with the belief that the power is off.

Voltage Feedback is another possibility, which, under certain circumstances, occurs when a motor fails.

This is more of a safety issue than anything else, but it's also possible that if both lines aren't switched, the owner of the device could be in violation of the law.

Any resulting injury could be very costly, in either case.

Joel






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 08-22-2007, 19:30 Post: 144925
Billy

TP Contributor

View my Photos

View my Photos  Pics
Join Date: Oct 1999
Location: Southeast Oklahoma
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 975

7
Filter by User
 Yamaha Generator problem

Now we're getting somewhere!

1) Nothing will happen......until somebody attempts to work on the motor, with the belief that the power is off.

Regardless of any kind of switch/s or how sophisticated, one should always make sure the power is off. That would be the same as replacing something as simple as a light switch.

2) Voltage Feedback is another possibility, which, under certain circumstances, occurs when a motor fails.

Don't know where you're going with this? If the motor fails, it fails regardless of whether this switch is on or off. What if it failed when the switch was on? There should be a breaker in there somewhere.

3) This is more of a safety issue than anything else, but it's also possible that if both lines aren't switched, the owner of the device could be in violation of the law.

This I will have to research but I'm almost certain of the answer. There's literally millions of motors wired with a single L 220v switch. I'll have to get back with you on this one.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
Reply | Pop Up Window Reply | Add PhotoAdd Photo


Page 1 | 2 | [ 3 ] | 4 |      << Prev | Next >>

Discussion Boards > Active Subjects > Messages as Posted > Generators Forum

Thread 144588 Filter by Poster:
8x56mn 4 | AnnBrush 1 | Billy 7 | candoarms 6 | earthwrks 1 | harvey 1 | JasonR 1 | kthompson 5 | Murf 6 |

 (advanced search)

Picture of the Day
DennisCTB

Current Events - House Fire Near Me
House Fire Near Me


Unanswered Questions

Gas Generator Weather Protecti
Horse Injured Polyrope Electri
Do electric fences keep out de
Any Peruvian Paso Owners Out T
gas powered post driver
My new born foal is really sic
Trailer Axle
dump trailer blueprints


Active Subjects

Gas Generator Weather Protecti
Went to see Dennis Reis this w
Signs to look for prior to lab
leg injury
Broodmare has welts all over h
Some Christmas Humor For Horse
poles in the ground vs. concre
ever thought about moving?


Hot Topics

new app owner
Some Christmas Humor For Horse
Any Peruvian Paso Owners Out T
Heating a Garage
Gas Generator Weather Protecti
Do electric fences keep out de
gas powered post driver
Trailer Axle


Featured Suppliers

Mountain Creek Labradoodles
      MountainCreekLabradoodles.com





New Forums on Gun Sport Shooting and Hunting -- BarrelPoint.com  New Forums on Horses ManePoint.com
Talk Horses at ManePoint
Hunting + Gun Sports at BarrelPoint



Most Viewed

+ 3 Pt PTO generators
+ Generator set up ideas wanted
+ PTO Generators Observations
+ PTO driven vs Gas engine
+ Best Portable Generator 7500W Review
+ PTO Horsepower and Generator Question
+ I love my Generator
+ Features to look for in stand alone generator
+ building budget auto-backup system
+ Yamaha Generator problem

Most Discussion

+ Generator set up ideas wanted
+ PTO Generators Observations
+ 3 Pt PTO generators
+ PTO Horsepower and Generator Q
+ I love my Generator
+ Features to look for in stand
+ Yamaha Generator problem
+ Best Portable Generator 7500W
+ Power stability with PTO gener
+ Measuring Frequency in a gener

Newest Topics

+ no electric power
+ Premium Fuel for Generator Avoid Ethanol Myth
+ How to increase Portable Generator Wattage output
+ Gillette vs Winco Generator Review
+ Best Portable Generator Temporary Shelter
+ Portable Generator House Backup Grounding
+ Dielectric antioxidant grease
+ Welder generator burning up tool switches
+ Welder generator burning up tool switches
+ PowerBoss Brush versus brushless Generators
















Turbochargers for Tractors and Industrial Machines
Cab Glass for Tractors and Industrial Machines

Alternators for Tractors and Industrial Machines
Radiators for Tractors and Industrial Machines

Driveline Components for Tractors and Industrial Machines
Starter Motors for Tractors and Industrial Machines