discussion   |   photos   |   email   |   myProfile   |   home          Login Now | Sign Up


Forum Index


New As Posted | Active Subjects



Click to Post a New Message!

Discussion Boards > Active Subjects > Messages as Posted > Generators Forum

Page [ 1 ] | 2 | | Next >>
Reply | Pop Up Window Reply | Add PhotoAdd Photo
 11-27-2003, 07:53 Post: 69765
harvey



View my Photos

View my Photos  Pics
Join Date: Sep 2000
Location: Moravia, NY
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 1534

4
Filter by User
 Transfer Switches

Have a pto gen on the way and working on the simplest way to tie into my power system...I'd appreciate info on how anyone else has tied theirs in.

I've been doing lots of research on transfer switches and power centers.

I still have not decided how I'll do it yet.

Here is a link to 1 of the most informative sites I've found. It has sechamatics and very good prices.






Link:   Click Here 

Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 11-27-2003, 19:12 Post: 69804
loghouse95



Join Date: Jul 2003
Location: missouri
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 87
 Transfer Switches

Harvey I am not sure this will be helpful but a few years back I in stalled a backup generator and transfer box The electric company came out and installed the transfer box for me at no charge, their reasoning, and I must say I agree with them,they wanted to make sure it was installed properly so one of their people would not get eletocuted... Might want to check with your electric company...Good Luck






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 11-27-2003, 19:31 Post: 69805
TomG

TP Contributor

Join Date: Feb 2002
Location: Upper Ottawa Valley
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 5406

3
Filter by User
 Transfer Switches

The first thing I'd say is to check with an electrical supplier that sells to contractors or your utility to find out what type units are approved. The equipment on the site you mentioned may well be fine, but just because something is UL approved doesn't mean a particular utility accepts it. An electrical supplier won't guarantee what they sell will pass inspection but what they handle ordinarily is approved for use in there area and they know what contractors buy.

To make sure were talking the same thing, when I say generator panel, I mean something that is wired as a branch circuit on a service panel. The entire service does not pass through such a panel, and that's what I have. When I say transfer panel I mean a unit that is installed in the service line and the entire service load flows through the unit. The site you mention may not use the same terminology. The site does seem to contain some hybrids of these two types. The automatic start type that manages the load seems interesting.

There are advantages to each type. In general, transfer switches feed the entire service panel and they do not disturb existing branch circuit wiring, but most people won't have a generator large enough to carry the entire normal load. The load must be managed by selectively turning off breakers. Installation of transfer switches ordinarily require a temporary service disconnect by the utility. Instillation can be messy for an underground service where the feed from the meter base goes into the back of a combination service panel. The choice can be either moving the panel or the meter.

Generator panels operate as a branch circuit and may provide up to 125A and more than 20 branch circuits. However, installing them does require moving circuits from the service to the generator panel and some lines almost always must be spliced and lengthened. My 60A -generator panel provides 20 circuits and was less expensive than a 200A transfer switch, but prices may have changed since backup power became more popular.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 11-28-2003, 19:50 Post: 69890
kadorken



Join Date: Jul 2003
Location: Canada
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 67

2
Filter by User
 Transfer Switches

I just replaced the old 200AMP service in my house with a 200AMP Federal Pioneer Generator Panel. I wired the crucial circuits (refrigeration, well pump, heating system, basic kitchen outlets) to the generator side of the panel.

There is a builtin 70AMP transfer/isolation switch in this panel, and plenty of room to expand.

Not sure if this particular brand/model is available everywhere. See the link for details.






Link:   Federal Pioneer Generator Panel 

Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 11-29-2003, 04:30 Post: 69912
harvey



View my Photos

View my Photos  Pics
Join Date: Sep 2000
Location: Moravia, NY
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 1534

4
Filter by User
 Transfer Switches

That is a nice arrangement.

I was somewhat suprised to see inches included in the specs. So they must be in bed with some company down here.

I have a fairly (15yrs) new 200amp service with 40 or so branch circuits not counting 2 sub panels.

Bottom line is: its gonna cost any way I go about it unless I backwire the main box (which is ill-eagle). I am looking at options and do appreciate the input.

But as I sit here thinking $3000 for a total system is kinda cheap insurance for the ability to do what I need to when the power is down. Of course I could do like women and go shopping.

Now how to hook it up SIMPLE!






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 11-29-2003, 06:05 Post: 69913
TomG

TP Contributor

Join Date: Feb 2002
Location: Upper Ottawa Valley
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 5406

3
Filter by User
 Transfer Switches

Harvey:

It's sort of ironic that I was about to comment before your reply was posted but was outside with a cigar when our power went down and knocked me off internet. So, here's your post first on the list after I get power back.

I've installed 3 new services, a number of new panels and sub-panels and a slew of branch circuits--all as my own contractor and all with permits and inspections. I've had no problems with the inspectors and they've been helpful if anything. Installing a generator panel on an existing service panel isn't a bad job and I think it's within the capabilities of many homeowners with a bit of study in a 'wiring made simple' book. The components required really aren't very expensive.

My generator panel also is a Federal panel. It sounds like they built basically the same panel I've got into a single 200A-combination panel. That sounds ideal if a new service panel is being installed as well and that's probably what I would have gotten if one had been available at the time.

I can't remember if it was Ken that had problems with an inspector but I've thought about that story. I wonder if the system was an automatic start type? If so, that may explain the inspector's attitude. The inspector limited the circuits on generator to the total peak load demands. You basically can't have many circuits on generator and use a small generator unless somebody's around to shut some circuits down. That's why the automatic power management panel on the site you mentioned sounded interesting (but it may not be approved everywhere).






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 11-29-2003, 07:14 Post: 69917
harvey



View my Photos

View my Photos  Pics
Join Date: Sep 2000
Location: Moravia, NY
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 1534

4
Filter by User
 Transfer Switches

I remember Kens problem. I do not like inspectors sticking their noses in my house. Iam adding on to her workshop again and pulled in a couple of more circuits for her machines. I sure do not need someone looking for my nailing specifications, engineer stamped blueprints or the little stamp grade on the cheap 2x4 that are non-load bearing. I'd probably go ballistic, then I'd have to put hoe on tractor to dispose of all the evidence.

Our towns can hire JOE-SHIT-THE-RAGMAN who does not have a clue about nothing except he read it in a book somewhere and believes it is the only way. Yes we have had some good inspectors that were helpful. But for the most part the majority around here suck.

The last time we got a permit for her shop we went thru ACCESSABILITY ISSUES. (I work with disabled kids during the winter so I am not against accessibility.) What I do have problems with is inspectors that do not have a clue and tell me what they think I need, plus all the stuff required by law that I would have to change or do and a special marked parking spot...

I do most/all of my wiring and if I error it is on the overkill side ie: all 12/2 for all circuits and not a lot of outlets per circuit and much heavier for the big ones.

If I go to the whole house switch that means power company to disconnect, an electrician to connect and an inspector to ok before power company rehooks. Of course inspectors have to stick their noses in parts they do not need to and some of the stuff may not be to exact code specs ie: staples not exactly 4-6" from boxes if that is the spec, I really can not see the concern.

I am leaning more to the sub panel arrangement. I have a 20kw PTO on the way it is more than enough to run everything I'll need for a outage or a prolonged outage (If we ever have one). I may get a small gas/diesel one also to run wood stove blowers (when needed) and a couple of lights at night, no appliances.

I am a little leary of the hotwire thing (backfeeding) because if I have the gen and am out of town or on the road she'll have one of the boys come over and hook up. So I might as well be on the safe side.

I see my inspector soapbox will need some rebuilding after the thrashing it just got!!!






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 11-29-2003, 08:08 Post: 69920
Billy

TP Contributor

View my Photos

View my Photos  Pics
Join Date: Oct 1999
Location: Southeast Oklahoma
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 975

2
Filter by User
 Transfer Switches

Why can't you use a simple 200 amp manual transfer switch, installed between the electric meter and the breaker box?






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 11-29-2003, 08:23 Post: 69921
harvey



View my Photos

View my Photos  Pics
Join Date: Sep 2000
Location: Moravia, NY
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 1534

4
Filter by User
 Transfer Switches

I'd have to have the power company disconnect an electrician to wire and a inspector to approve b4 reconection. C above.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 11-29-2003, 09:06 Post: 69924
Billy

TP Contributor

View my Photos

View my Photos  Pics
Join Date: Oct 1999
Location: Southeast Oklahoma
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 975

2
Filter by User
 Transfer Switches

It would be nice to have a licensed electrician friend. Or maybe a friend that is friends with one Laughing out loud

I'm thinking here but if you get a permit (if it's required) to install a transfer switch. Wouldn't the only thing up for inspection be the installation of that switch?






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
Reply | Pop Up Window Reply | Add PhotoAdd Photo


Page [ 1 ] | 2 | | Next >>

Discussion Boards > Active Subjects > Messages as Posted > Generators Forum

Thread 69765 Filter by Poster:
Billy 2 | Chief 1 | harvey 4 | kadorken 2 | kwschumm 1 | loghouse95 1 | TomG 3 |

 (advanced search)

Picture of the Day
candoarms

Landscape Maintenance - Elm Tree Removal Minot North Dakota
Elm Tree Removal Minot North Dakota


Unanswered Questions

Gas Generator Weather Protecti
Horse Injured Polyrope Electri
Do electric fences keep out de
Any Peruvian Paso Owners Out T
gas powered post driver
My new born foal is really sic
Trailer Axle
dump trailer blueprints


Active Subjects

Gas Generator Weather Protecti
Went to see Dennis Reis this w
Signs to look for prior to lab
leg injury
Broodmare has welts all over h
Some Christmas Humor For Horse
poles in the ground vs. concre
ever thought about moving?


Hot Topics

new app owner
Some Christmas Humor For Horse
Any Peruvian Paso Owners Out T
Heating a Garage
Gas Generator Weather Protecti
Do electric fences keep out de
gas powered post driver
Trailer Axle


Featured Suppliers

Mountain Creek Labradoodles
      MountainCreekLabradoodles.com





New Forums on Gun Sport Shooting and Hunting -- BarrelPoint.com  New Forums on Horses ManePoint.com
Talk Horses at ManePoint
Hunting + Gun Sports at BarrelPoint



Most Viewed

+ 3 Pt PTO generators
+ Generator set up ideas wanted
+ PTO Generators Observations
+ PTO driven vs Gas engine
+ Best Portable Generator 7500W Review
+ PTO Horsepower and Generator Question
+ I love my Generator
+ Features to look for in stand alone generator
+ building budget auto-backup system
+ Yamaha Generator problem

Most Discussion

+ Generator set up ideas wanted
+ PTO Generators Observations
+ 3 Pt PTO generators
+ PTO Horsepower and Generator Q
+ I love my Generator
+ Features to look for in stand
+ Yamaha Generator problem
+ Best Portable Generator 7500W
+ Power stability with PTO gener
+ Measuring Frequency in a gener

Newest Topics

+ no electric power
+ Premium Fuel for Generator Avoid Ethanol Myth
+ How to increase Portable Generator Wattage output
+ Gillette vs Winco Generator Review
+ Best Portable Generator Temporary Shelter
+ Portable Generator House Backup Grounding
+ Dielectric antioxidant grease
+ Welder generator burning up tool switches
+ Welder generator burning up tool switches
+ PowerBoss Brush versus brushless Generators
















Turbochargers for Tractors and Industrial Machines
Cab Glass for Tractors and Industrial Machines

Alternators for Tractors and Industrial Machines
Radiators for Tractors and Industrial Machines

Driveline Components for Tractors and Industrial Machines
Starter Motors for Tractors and Industrial Machines