 11-14-2006, 21:20 Post: 136907
brokenarrow



Join Date: Jan 2004
Location: Wisconsin
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 1288
 ground wireing

Whats better to use, black 1 1/2 or 2" pottable water pipe (plastic), or the white glue together pvc?
I was leaning towards the pvc because it seams it would be easy and water tight to put in "t"'s to the surface verse the black tubing although the black tubing would be great for long runs?
I plan on laying 500 foot of under ground electric. Was planning to run it down my driveway and have several poles with lights and or security camersa on em (not that I need security but it would be nice when you hear a car on gravel to be able to see what or who it is?)
Any suggestions before I spend a day reading back posts?
Also, is it a very good idea to keep it water tight? I was thinking, maybe that would be real important






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 11-14-2006, 22:07 Post: 136908
kwschumm



View my Photos

View my Photos  Pics
Join Date: Feb 2003
Location: NW Oregon
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 5764
 ground wireing

I don't think underground runs are normally expected to stay 100% dry. Water will always find a way in, so you need to use underground rated wiring. The conduit is more to protect against chafing, rocks, etc. I'm no electrician but that's what I've heard and read. Be sure to take voltage drops over long runs into consideration when you size the wiring. I know that underground low voltage cable is "flooded" with a gooey silicone like substance to protect against water and it wouldn't surprise me to find high voltage UF (?) cabling is similar.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 11-14-2006, 22:14 Post: 136909
MiikeJD



Join Date: Nov 2003
Location: Southern Illinois
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 25
 ground wireing

I use grey plastic conduit for buried runs. I also use direct bury wire in the conduit. I usually buy it at Lowes or Home Depot. There are a lot of boxes and fittings that are made for the conduit. I also leave a pull string in the conduit in case I need to pull additional wires for future use. Hope this helps you.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 11-15-2006, 06:04 Post: 136913
hardwood

TP Contributor

Join Date: Dec 2002
Location: iowa
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 3582

2
Filter by User
 ground wireing

I think we can get to an overkill level on buried wires at times. The first buried wire I put in at the farm was just common underground rated wire in a trench, then as time went along we kept adding runs here and there to new buildings or bins as needed. The last runs we buried were in underground conduit. My point being that the 35 year old direct bury runs have worked fine so maybe that's all we really need in the first place. An electrician friend of mine who put in the last couple runs laid a yellow caution tape about a foot under the surface for a safety measure, i thought that was a good idea. Frank.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 11-15-2006, 06:31 Post: 136914
earthwrks

TP Contributor

View my Photos

View my Photos  Pics
Join Date: Dec 2003
Location: Home Office in Flat Rock, Michigan
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 3853
 ground wireing

I'v seen guys use the black 4" corrugated non-perforated drain pipe---cheap and easy to dig up and cut a hole in to access the pipeline to install a branch line. Of course all wire and connections would have to be waterproof. And to run a line, tie a close-fitting rag on a string and pull or push it with a shopvcac or air compressor. Which leads me to my next point: If you plan on having poles or any branch lines off the main one, unless you use electric-rated, glue-type, gray pipe, and the large-sweep radius elbows, you'll kick yourself when it comes time to pull cable due to hanging up on the edges of regular, small radius pipe and connections (been there). The caution tape hardwood mentioned is Code where I'm from. Except the tape has to be a foot above the line so that the excavator knows he's very close to hitting it then have a helper hand-dig, rather than finding the tape a foot below ground and guessing when he'll find it---BBBVvvvvvzzZZZZPOW! (my impression of how an electric line sounds when hit by a backhoe bucket)

And as far as cameras go, you might want to consider battery-powered wireless ones. And I think there are solar-powered ones too.

Lowes has solar-powered security lights too.

Broken, did you end up buying a skid steer? You might want to check out eBay--there are many that are going for many, many thousands cheaper than what the dealer gave me for trade in on my LS180 ($20,000)---I've seen some in the range of $12,000-15,000 in very good shape.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 11-15-2006, 07:03 Post: 136916
JAZAK5



Join Date: Jul 2003
Location: coxsackie,ny
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 276
 ground wireing

I know that code in my area is
0-18 inches under grade: metal conduit

18 inches to 24 inches :plastic schedule 40 which is ALOT tougher than black plastic pipe /it's crush resistance would be highly recommended near a driveway

You can direct bury as long you have 6 inches of fine sand as a base and cover below 24 inches of grade how ever you can not back fill with rocks larger than fist size.

in my area thats immpossible,conduit is run every where its cheaper than fill and the man hours






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 11-15-2006, 07:09 Post: 136917
hardwood

TP Contributor

Join Date: Dec 2002
Location: iowa
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 3582

2
Filter by User
 ground wireing

I just remembered something I saw just yesterday that did'nt look good to me. Someone is building a house down the road from us on a pretty big lot probably 500 ft. deep and the same wide. The house is at the far side of the lot with the driveway running parallel close to the east lot line to the house. Yesterday the power co. was there puting in the service. They ran the buried line from the house diagional across the lot to the opposite corner where the pole is at the road. I think the power co. gives you the first 50 or 75 ft. then the rest is your expense, so I suppose they took the most direct route to save on the footage. My immediate thought was that sooner or later the home owner will want a shed, pool, horse barn, etc., and guess what will be right where they want the building. If it were mine I would want the power line along side of the drive where it would likely never be in the way. Frank.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 11-15-2006, 09:05 Post: 136920
kyvette

TP Contributor

View my Photos

View my Photos  Pics
Join Date: Feb 2004
Location: Central Kentucky
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 194
 ground wireing

Broken,
I would recommend using schedule 40 PVC conduit. It is normally stock in 10ft lengths but, you can sometimes get it in 20ft lengths. I would also recommend a depth of 36". This exceeds NEC depth requirements, but will add additional protection. The warning tape is also a good idea and should be about 12" below final grade.

You cannot keep water out of conduits, therefore use conductors rated for wet locations. I would suggest junction boxes at the base of each pole.

Hopes this helps, Dave






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 11-15-2006, 09:31 Post: 136923
Murf



View my Photos

View my Photos  Pics
Join Date: Dec 1999
Location: Toronto Area, Ontario, Canada
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 7054
 ground wireing

Dave's right, you will never keep the wires dry, so don't even waste your time trying.

Use the Sced. 40 conduit, it's cheap insurance compared to digging it up when a rock or tree root breaks the line.

There is often very little price difference to up grade one size, if you do, buy a spool of light rope to put in with the wiring, if you ever decide to add another wire, you will be *very* glad you have that wire there to pull the new cable through. If you do put a second wire in, be sure to pull a piece of heavy twine through with it, you can then use the twine to pull the rope back in place for next time.

Best of luck.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
Reply | Pop Up Window Reply | Add PhotoAdd Photo


Page [ 1 ] |

Discussion Boards > Active Subjects > Messages as Posted > Electric Forum

Thread 136907 Filter by Poster:
brokenarrow 1 | earthwrks 1 | hardwood 2 | JAZAK5 1 | kwschumm 1 | kyvette 1 | MiikeJD 1 | Murf 1 |

 (advanced search)

Picture of the Day
minimac

Gas Power Tools - How do you sharpen chain saw chain
How do you sharpen chain saw chain


Unanswered Questions

Gas Generator Weather Protecti
Horse Injured Polyrope Electri
Do electric fences keep out de
Any Peruvian Paso Owners Out T
gas powered post driver
My new born foal is really sic
Trailer Axle
dump trailer blueprints


Active Subjects

Gas Generator Weather Protecti
Went to see Dennis Reis this w
Signs to look for prior to lab
leg injury
Broodmare has welts all over h
Some Christmas Humor For Horse
poles in the ground vs. concre
ever thought about moving?


Hot Topics

new app owner
Some Christmas Humor For Horse
Any Peruvian Paso Owners Out T
Heating a Garage
Gas Generator Weather Protecti
Do electric fences keep out de
gas powered post driver
Trailer Axle


Featured Suppliers

Mountain Creek Labradoodles
      MountainCreekLabradoodles.com





New Forums on Gun Sport Shooting and Hunting -- BarrelPoint.com  New Forums on Horses ManePoint.com
Talk Horses at ManePoint
Hunting + Gun Sports at BarrelPoint



Most Viewed

+ Hanging Ceiling Fan in Great room
+ Back-up power
+ need a 110V winch
+ Underground Elec - direct-burial vs in conduit
+ trouble shooting
+ Underground Wiring
+ Better common light bulbs
+ Tapping in to Well Electric
+ pole barn sub panel
+ wiring my new garage

Most Discussion

+ need a 110V winch
+ pole barn sub panel
+ Hanging Ceiling Fan in Great r
+ Back-up power
+ Turn a freezer into a refriger
+ Underground Wiring
+ trouble shooting
+ wiring my new garage
+ Tapping in to Well Electric
+ Electrical Ground Question

Newest Topics

+ LED light bulb hum
+ Breaker Trips After lIghts on 30 minutes
+ Power 120v heat strip off one phase of 240v line
+ Maytag Oven
+ trouble shooting
+ Infrared space heaters
+ T-8 s or T-12 s
+ lighting
+ noalox compound
+ 220 pump shed
















Turbochargers for Tractors and Industrial Machines
Cab Glass for Tractors and Industrial Machines

Alternators for Tractors and Industrial Machines
Radiators for Tractors and Industrial Machines

Driveline Components for Tractors and Industrial Machines
Starter Motors for Tractors and Industrial Machines