 Underground Wiring

I have a garage that is 200' from my closest power source (my cabin) I use a 250' piece of 12ga house wire right now with plug ins on the ends when I need power out there. As you probably can imagine that is getting old, rolling it out every time I am there and back up again when I leave not to mention the hassek everytime I want to move equipment from garage to house or for field work.
I am moving in less than 5 years to this place and plan to build a house attatched to the cabin along with anouther garage. When I do move and build I will be using this garage for 110 everyday while building the house. I also have never had electric strung out there in winter (ever) and that makes it a pain when cutting up deer or what ever!
I have been around this block once before so I am not making the same mistakes twice!

Would it be ok to run a uf wire underground from the house to the garage and (temporarily) only put it 12" under the ground? My thinking is to put in a post next to the cabin with an outdoor box on it that I could hook up a short extension cord to to provide power out to the garage. This way here I would only have the cost of the wire and box that I would eat in a few years. Untill then I would only be using the electric for small hand tools maybe a table saw or chop saw sporadically and a few flouresent lights.
I plan on making part of this garage into a workshop and may add on to it so I really dont want to wire it up yet because my plans may change.
How un-safe would it be to run the wire the way I said?
We have NO zoning/inspections where I live so I would like to be half way safe yet dont want to spend too much and eat it later.
Thanks
TOM






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 07-05-2004, 19:51 Post: 90140
harvey



View my Photos

View my Photos  Pics
Join Date: Sep 2000
Location: Moravia, NY
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 1534

2
Filter by User
 Underground Wiring

You can run UF under ground. Most of my yard lights and the run to my shed is in UF. The shed is 180' from house and is on 12/2 power it is a little iffy for large circular saws.

Very few of my wires like that are more than 6-8 inches down. I did draw out maps for the next residents after I do not need this stuff anymore... Smile

Nothing pissed me off more than having to make a trip to the shed for some obscure part I packed away because it might come in handy some day and have to search with a flashlight for it...

Good Luck Harvey






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 07-05-2004, 20:39 Post: 90145
JAZAK5



Join Date: Jul 2003
Location: coxsackie,ny
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 276
 Underground Wiring

200' is really "iffy" on 12/2 your lucky to get 10 amps with out dimming your flouro lights.

run 10/2 and a 20 amp breaker that should run a 3-5hp compressor intermediatly.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 07-05-2004, 21:45 Post: 90150
loghouse95



Join Date: Jul 2003
Location: missouri
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 87

3
Filter by User
 Underground Wiring

I think you are asking for a lot a trouble trying to run any power tool on what is essentially a 200 foot 12-2 extension cord. At 10 amps The one way distance for an acceptable 2% voltage drop is only 70 feet Trying to run 180 feet you will very likely burn a motor up.. Remember a 1hp motor electric motor needs around 2200 hundred watts of surge to get started. You might want to consider running 220 volts to a sub-panel at your garage.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 07-05-2004, 22:07 Post: 90154
brokenarrow



Join Date: Jan 2004
Location: Wisconsin
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 1288

7
Filter by User
 Underground Wiring

Log houses and other here
This is the kind of info I want. I had used that extension cord while building the garage and it just keeps coming out everytime I need it. So far I only used it for small compressor (nail gun and buzz saw work) I dont plan on using it for the burial since that wire is not uf and also I did not think it was large enough for what I need it for over the next 5 years.
I am looking for the cheapest way to get power out to the garage to run a table saw (sporadically while building my newer house portion) but mostly for lighting in the garage and maybe a buzz saw.? I am NOT planning on keeping this set up. after I build I will run a main line with 220 to a panel. I just dont want to jump the gun and run power to a spot that I may need to move in the future. Also I dont know exactly where other utilitys will be so I may have to dig up the electric source later. That is why I dont want to do it right (the first time) SO
What would you run for a 200 foot run for what I described if you wanted it to be expendable in a few years?
Thanks again






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 07-05-2004, 22:49 Post: 90159
loghouse95



Join Date: Jul 2003
Location: missouri
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 87

3
Filter by User
 Underground Wiring

Brokenarrow I sure wish I could recommend a cheap and safe way but....... By your reply I assume you are going to need a minimum of 2400 watts i.e., Table saw, lights... I would recommend running 10-3 with ground from your main breaker box. this will give you 220 volts and a acceptable 2% drop in voltage at 225 feet, this would provide with the power you will need and you could use the wire and sub-panel later on for other projects.... Good luck






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 07-06-2004, 00:33 Post: 90166
AV8R



View my Photos

View my Photos  Pics
Join Date: Oct 2003
Location: North Central Wisconsin
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 882
 Underground Wiring

Arrow: I agree with Loghouse, please use the (10-3) 220v and mount a small temporary breaker box. My neighbor buried a small (12-2) 110v line and ran it about 250 feet to a shed in the back yard. The fire inspector said the cause was electrical. House was a total loss.

I went with a complete 2nd service to a 200 amp panal in the workshop because my main house 200 amp service was full. Watching the house acrossed the street burn kind of put the fear of God in me.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 07-06-2004, 06:30 Post: 90171
TomG

TP Contributor

Join Date: Feb 2002
Location: Upper Ottawa Valley
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 5406

3
Filter by User
 Underground Wiring

I have over 100' of 100A flex line to a 100A service panel that's mounted on plywood. Various receptacles are wired to the panel and also mounted on the plywood. I used it in the sound buz when a stage didn't have adequate AC. Bare ends were on the feed end of the flex line and were 'tied' into a service panel rails with clamps. The flex line had to be adequately protected. That's a fairly inexpensive way to get many 110V and 220V circuits temporary locations for weekend festivals and it would good enough to get passed fire marshals. The 110V receptacles used for on-stage circuits were GFI protected.

Since the sound buz days, I replaced the bare ends of the feed with a 30A 220V plug for my generator. The line and panel is overkill but it's something I already had. I'd check local regs but maybe something like 8-gauge flex line from a drier recpetical into a 30A subpanel (with it's own disconnect and the neutral/ground bond removed) would suit your needs. The flex line isn't exactly cheap though but it might remain useful if a remote work site had to be supported from a generator.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 07-06-2004, 07:38 Post: 90178
Murf



View my Photos

View my Photos  Pics
Join Date: Dec 1999
Location: Toronto Area, Ontario, Canada
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 7054
 Underground Wiring

Tom, maybe I'm missing something here, maybe I just haven't had enough coffee yet.

If it's only 200', and it's only going to be temporary anyway, why bury it at all?

It seems it would be a lot less work to put 2 poles & makeshift anchors in the ground than to trench 200' and I know the wire will cost a LOT less.

If there is an electrical contractor in the area go and talk to them. You will need some pro help once you start building anyway, most have poles, temporary service panels and rolls of used wire for putting up on job-sites like yours. For a few bucks they will often 'rent' them to you, especially if they get the work to do your new place.

Best of luck.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 07-06-2004, 19:20 Post: 90238
TomG

TP Contributor

Join Date: Feb 2002
Location: Upper Ottawa Valley
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 5406

3
Filter by User
 Underground Wiring

Murf: Sorry I wasn't more clear. The idea of flex line is not to bury it. Just drag the line to the house and plug it into a drier outlet as needed. Some planking might be needed in traffic areas.

That's the way it's done in the sound buz and without contractors or permits. Technically it does take an electrician to tap into the rails of a service sub-panel though, but in this case an existing receptacle would be used. However, the idea should be checked with officials to see if it'd fly in a particular area. It's basically just a heavy-duty extension cord that might have some on-going use. The panel could be used as a sub-panel in the permanent wiring.

Overhead line might even be cheaper. It may also start looking more like a permanent installation and be more subject to code--don't know about that though. What ever is done should be safe and not run afoul of insurance or regs.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
Reply | Pop Up Window Reply | Add PhotoAdd Photo


Page [ 1 ] | 2 | 3 | | Next >>

Discussion Boards > Active Subjects > Messages as Posted > Electric Forum

Thread 90124 Filter by Poster:
AV8R 1 | brokenarrow 7 | dkheckmanl 1 | harvey 2 | JAZAK5 1 | loghouse95 3 | Murf 1 | steve4300 1 | TomG 3 | WillieH 1 |

 (advanced search)

Picture of the Day
candoarms

Landscape Maintenance - Elm Tree Removal Minot North Dakota
Elm Tree Removal Minot North Dakota


Unanswered Questions

Gas Generator Weather Protecti
Horse Injured Polyrope Electri
Do electric fences keep out de
Any Peruvian Paso Owners Out T
gas powered post driver
My new born foal is really sic
Trailer Axle
dump trailer blueprints


Active Subjects

Gas Generator Weather Protecti
Went to see Dennis Reis this w
Signs to look for prior to lab
leg injury
Broodmare has welts all over h
Some Christmas Humor For Horse
poles in the ground vs. concre
ever thought about moving?


Hot Topics

new app owner
Some Christmas Humor For Horse
Any Peruvian Paso Owners Out T
Heating a Garage
Gas Generator Weather Protecti
Do electric fences keep out de
gas powered post driver
Trailer Axle


Featured Suppliers

Mountain Creek Labradoodles
      MountainCreekLabradoodles.com





New Forums on Gun Sport Shooting and Hunting -- BarrelPoint.com  New Forums on Horses ManePoint.com
Talk Horses at ManePoint
Hunting + Gun Sports at BarrelPoint



Most Viewed

+ Hanging Ceiling Fan in Great room
+ Back-up power
+ need a 110V winch
+ Underground Elec - direct-burial vs in conduit
+ trouble shooting
+ Underground Wiring
+ Better common light bulbs
+ Tapping in to Well Electric
+ pole barn sub panel
+ wiring my new garage

Most Discussion

+ need a 110V winch
+ pole barn sub panel
+ Hanging Ceiling Fan in Great r
+ Back-up power
+ Turn a freezer into a refriger
+ Underground Wiring
+ trouble shooting
+ wiring my new garage
+ Tapping in to Well Electric
+ Electrical Ground Question

Newest Topics

+ LED light bulb hum
+ Breaker Trips After lIghts on 30 minutes
+ Power 120v heat strip off one phase of 240v line
+ Maytag Oven
+ trouble shooting
+ Infrared space heaters
+ T-8 s or T-12 s
+ lighting
+ noalox compound
+ 220 pump shed
















Turbochargers for Tractors and Industrial Machines
Cab Glass for Tractors and Industrial Machines

Alternators for Tractors and Industrial Machines
Radiators for Tractors and Industrial Machines

Driveline Components for Tractors and Industrial Machines
Starter Motors for Tractors and Industrial Machines