 pole barn sub panel

Eric,
I thought I sent this from dial up connection but it did not make it.

In going over what you first asked, I have a question. Your two hot wires are 220 voltage across them, correct? If you used a side by side double breaker they should be 220. If you used a piggy back or two single breakers that are not side by side you may have both hot wires on the same leg of your main breaker box. If you do you only have 110 voltage and you are placing a double load on your single neutral. THAT WOULD BE DANGEROUS AND ONE DAY WILL FAIL.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 12-01-2005, 17:51 Post: 120229
EricBX1500



Join Date: Jul 2005
Location: mich
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 46

8
Filter by User
 pole barn sub panel

Kthompson, my sub is fed by a 30amp double pole breaker.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 12-01-2005, 20:32 Post: 120239
steve4300

TP Contributor

Join Date: Dec 2004
Location: NH
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 71

3
Filter by User
 pole barn sub panel

My best suggestion would to contact a good local electrician , the reason they make code rules is because someone before you has found out the hard way the wrong way to wire something.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 12-02-2005, 07:12 Post: 120257
kthompson



View my Photos

View my Photos  Pics
Join Date: Oct 2005
Location: South Carolina
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 5139

4
Filter by User
 pole barn sub panel

Eric,
I thought you probably had but I have seen the other done.

I hope you enjoy your barn.


As to codes there is reasons for them. Some even make a lot of sense which I fully agree. Now why was the code for years on a 110 circuit a power and a neutral or the black and white wire only? Then there came the smaller guage ground and then it was decided the ground must be as large as the power.

At the same time there was code requirement for the 110 circuit to have the third wire the ground as the same guage as the power and neutral the code also said if you were to replace the outlet itself in an old 2 wire circuit you were to use or at least allowed to use the 3 prong outlet giving the impression to someone using it to be a grounded outlet. Now if that makes sense I forgive those who make codes and think they are perfect. Some of the electric codes (last I studied them) were a lot like some of the IRS code, law but huh?

As to a good local electrician, please if you do, do ask more at least two and let us know if both gave the exact same answer. Now, let one be about 30 and one about 60. Don't forget to ask how many barns, houses or what ever each has wired and then how many have burnt due to wiring.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 12-07-2005, 17:56 Post: 120638
kully560
2005-12-07 00:00:00
Post: 120638
 pole barn sub panel

there is specific chapters in the nec on multi.outbuildings for farm use. local codes will superseed nec. for nec specs you do not need the ground wire for each building they will be treated as own sep. service and 2 grounds 6 feet apart. 6 throws of the hand still applies for any service.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 12-15-2005, 16:49 Post: 121135
Wen



Join Date: Jun 1999
Location: Texas
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 10

2
Filter by User
 pole barn sub panel

You should run a fourth wire (also #8) for the ground wire. Since the 30 amp circuit normally will be used to power other 15 or 20 amp circuits, a small 4 - 8 circuit breaker panel (without a main breaker is about $15 (plus $3/breaker) is required at the barn. It is also necessary to have a separate ground buss (normally purchased separately from the panel) for all ground returns. It is never permitted to use the neutral and ground busses tied together in a sub panel such as you are installing. Barn circuits should be protected by 15A or 20A GFCI circuits ($10) unless they are for (and ONLY for) dedicated fixed equipment. It is not expensive to conform to the NEC and much safer for everyone. The breakers allow you to turn off each circuit and the 30A breaker in the main panel allows you to disable the entire sub-panel in the barn. The correct wiring of ground and neutral wires allows the GFCI protectors to prevent shocks with nearby water and wet soil or concrete and are required.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 12-15-2005, 18:31 Post: 121137
EricBX1500



Join Date: Jul 2005
Location: mich
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 46

8
Filter by User
 pole barn sub panel

It is never permitted to use the neutral and ground busses tied together in a sub panel such as you are installing.




Actually it is permitted. Nec does state this, and was also confirmed by an electrician.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 12-15-2005, 21:39 Post: 121144
Wen



Join Date: Jun 1999
Location: Texas
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 10

2
Filter by User
 pole barn sub panel

The reason the NEC was changed was to be certain that ground fault interrupt devices would operate properly from sub-panel circuits and to prevent poor bonding to the neutral wire which can easily create a shock hazzard in damp locations. This separates the requirements for grounding and bonding at sub-panels. Metal pipes or ground rods are bonding to the ground (not the neutral) buss in the sub-panels.

A good internet reference on NEC Article 250.4 is located at "http://www.iaei.org/magazine/03_f/03_f_threechiefs.htm". It describes the installation detailed in the first post and provides step by step details on adding the fourth (ground wire) and why the isolation must be done in existing installations.






Link:   Click Here 

Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 12-16-2005, 19:21 Post: 121200
EricBX1500



Join Date: Jul 2005
Location: mich
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 46

8
Filter by User
 pole barn sub panel

That is true. Since I have only three feeds two hots and a neutral to the detached structure this is why I must bond the panel. If I don’t bond it and I have a ground fault more then likely this would not trip the breaker in the barn since earth is a terrible conductor of electricity. Now with me bonding the neutral and ground the ground fault will travel back to my main panel via the neutral which will give it enough resistance to trip the breaker. This is why I must bond the panel in the pole barn.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 12-23-2005, 09:24 Post: 121611
Carldarnell



Join Date: Dec 2005
Location: Taylorsville Ky
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 91

6
Filter by User
 pole barn sub panel

I am in Ky and wired my pole barn in 2004. The inspector told me to run two hot and one neutral to the barn to a panel with a 100amp breaker that feeds a box for 8 breakers. He said I do not need a bare ground wire with the service line to the barn nor a grnd rod to ground the service at the barn. The service is set up with an isolated neutral and the bare wires grounded to the breaker boxes. The two breaker boxes are bolted and grounded to each other. Ky addopted the 2005 NEC code in 2005 so it may be different now. I am going to ask around and see if I need a ground rod and any changes to the way it is hooked up. I am very currious and interested about this now.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
Reply | Pop Up Window Reply | Add PhotoAdd Photo


Page 1 | [ 2 ] | 3 |      << Prev | Next >>

Discussion Boards > Active Subjects > Messages as Posted > Electric Forum

Thread 119554 Filter by Poster:
kully560 1 | Carldarnell 6 | Chief 1 | Deereman 4 | EricBX1500 8 | kthompson 4 | kwschumm 1 | steve4300 3 | Wen 2 |

 (advanced search)

Picture of the Day
brewdog

Site Members - brewdog - NW PA - NH 3040  Woods Hoe  Woods Mower  Woods Brush Hog
brewdog - NW PA - NH 3040 Woods Hoe Woods Mower Woods Brush Hog


Unanswered Questions

Gas Generator Weather Protecti
Horse Injured Polyrope Electri
Do electric fences keep out de
Any Peruvian Paso Owners Out T
gas powered post driver
My new born foal is really sic
Trailer Axle
dump trailer blueprints


Active Subjects

Gas Generator Weather Protecti
Went to see Dennis Reis this w
Signs to look for prior to lab
leg injury
Broodmare has welts all over h
Some Christmas Humor For Horse
poles in the ground vs. concre
ever thought about moving?


Hot Topics

new app owner
Some Christmas Humor For Horse
Any Peruvian Paso Owners Out T
Heating a Garage
Gas Generator Weather Protecti
Do electric fences keep out de
gas powered post driver
Trailer Axle


Featured Suppliers

Mountain Creek Labradoodles
      MountainCreekLabradoodles.com





New Forums on Gun Sport Shooting and Hunting -- BarrelPoint.com  New Forums on Horses ManePoint.com
Talk Horses at ManePoint
Hunting + Gun Sports at BarrelPoint



Most Viewed

+ Hanging Ceiling Fan in Great room
+ Back-up power
+ need a 110V winch
+ trouble shooting
+ Underground Elec - direct-burial vs in conduit
+ Underground Wiring
+ Tapping in to Well Electric
+ pole barn sub panel
+ Better common light bulbs
+ wiring my new garage

Most Discussion

+ need a 110V winch
+ pole barn sub panel
+ Hanging Ceiling Fan in Great r
+ Back-up power
+ Turn a freezer into a refriger
+ Underground Wiring
+ trouble shooting
+ wiring my new garage
+ Tapping in to Well Electric
+ Electrical Ground Question

Newest Topics

+ LED light bulb hum
+ Breaker Trips After lIghts on 30 minutes
+ Power 120v heat strip off one phase of 240v line
+ Maytag Oven
+ trouble shooting
+ Infrared space heaters
+ T-8 s or T-12 s
+ lighting
+ noalox compound
+ 220 pump shed
















Turbochargers for Tractors and Industrial Machines
Cab Glass for Tractors and Industrial Machines

Alternators for Tractors and Industrial Machines
Radiators for Tractors and Industrial Machines

Driveline Components for Tractors and Industrial Machines
Starter Motors for Tractors and Industrial Machines