 Electrical Ground Question

I have poultry houses with some pretty expensive electronic equipment. It's not uncommon for electrical shorts to occur from time to time. The neutral and ground bars are bonded together inside the breaker box (3 wire system). Would it be better to separate the neutral and ground bars and run the ground bar directly to a ground rod?






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 03-03-2006, 13:02 Post: 125499
Peters

TP Contributor

View my Photos

View my Photos  Pics
Join Date: Feb 2002
Location: Northern AL
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 3034
 Electrical Ground Question

There should be a ground rod from the neutral to the ground of the meter plate. Normally the ground and neutral are strung together. If you separated them only difference would be that neutral will be connected to the ground at the house box and the other is grounded at the pole.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 03-03-2006, 13:41 Post: 125503
greg_g



View my Photos

View my Photos  Pics
Join Date: Jan 2004
Location: Western Kentucky
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 1816

4
Filter by User
 Electrical Ground Question

I wouldn't mess with the the breaker box wiring at all, besides - there's probably a code violation in there somewhere. If the issues you're experiencing are due to moisture, I'd recommend some GFI breakers. If the issues are due to supply problems, I'd go with surge suppressors. For the really sensitive (or expensive) stuff, I use an UPS with line conditioning.

//greg//






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 03-03-2006, 14:01 Post: 125504
Billy

TP Contributor

View my Photos

View my Photos  Pics
Join Date: Oct 1999
Location: Southeast Oklahoma
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 975

5
Filter by User
 Electrical Ground Question

Let me add something to this scenario. You might say, the rest of the story or real story. When they were wiring up these control rooms, the electrician told his helper to cut the neutral/ground bonding bar out. The neutral wires are attached to the neutral bar, the ground wires are attached to the ground bar. The neutral bar is tied to the power company neutral. BUT, the ground bar isn't tied to shit.

Should I

A) run a jumper from the neutral bar to ground bar

B) run a wire from the ground bar to a ground rod.

C) Do both






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 03-03-2006, 14:03 Post: 125505
kthompson



View my Photos

View my Photos  Pics
Join Date: Oct 2005
Location: South Carolina
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 5139
 Electrical Ground Question

Billy,

I had office once that had problems with electronics going out all the time, some even with surge protectors on them. Lady working me had worked for local power company and said get the surge protector that goes between meter and base. It solved the problem. If your power company has them they must install them.

I agree with the advice Peters and Greg have also given.

kt






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 03-03-2006, 16:28 Post: 125515
greg_g



View my Photos

View my Photos  Pics
Join Date: Jan 2004
Location: Western Kentucky
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 1816

4
Filter by User
 Electrical Ground Question

I gotta say I don't understand "the rest of the story", but maybe there's some state/local code in Oklahoma that applies. At this point I cannot justifiably recommend any action to be taken at the box, without knowing more of the "why". Did you phone the electrician for an explanation?

Is this breaker box supplied through a it's own service entrance and meter? Or through the meter that serves the rest of the building(s)? If the latter, it would seem to me that soome of the electrical problems in the chicken coop might be due to mismatched ground potential.

//greg//






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 03-03-2006, 21:09 Post: 125534
JD855inWI



Join Date: Aug 2004
Location: Mid East Wisconsin
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 38
 Electrical Ground Question

Problems could be caused by circulating currents or ground loops. A hen house has a corrosive atmosphere which could attack grounding connections in conduits and panels. The neutral and the ground should only be bonded (tied together) at one point. Some municipalities this is in the meter socket others in the main circuit breaker panel. If the control room panel is sub-fed from a main panel, then the neutrals and the grounds must be separated in the sub-panel. The sub-panel would be fed with 4 wires from the main panel. Check for a bonding screw in the neutral bar, threaded through the bar into the metal panel frame. A more detailed explanation of the complete system and the type of problem would help.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 03-04-2006, 21:07 Post: 125563
steve4300

TP Contributor

Join Date: Dec 2004
Location: NH
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 71

2
Filter by User
 Electrical Ground Question

Billy something does not seem right.I think I would call a different Electrician to look at it. The neutral and ground should not be seperated unless it is a sub panel. Also somewhere on main service there should be a ground rod also there should be a bonging ground to the wire mesh or rebars in footings.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 03-04-2006, 22:11 Post: 125567
Billy

TP Contributor

View my Photos

View my Photos  Pics
Join Date: Oct 1999
Location: Southeast Oklahoma
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 975

5
Filter by User
 Electrical Ground Question

I called him today and he said "he thought" I had a 4 wire system. Since his helper cut out the bonding bar, to drive a ground rod and tie the ground bar to it and to leave the neutral bar tied to power company neutral.

I talked to another electrician and he suggested I do the same.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 03-05-2006, 08:15 Post: 125580
brokenarrow



Join Date: Jan 2004
Location: Wisconsin
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 1288
 Electrical Ground Question

Billy
Glad you found where your problem really exists! I suggest that the electrician come out and "drive the ground bar and the rest of the work" Also maybe buy you a lunch and a handshake.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
Reply | Pop Up Window Reply | Add PhotoAdd Photo


Page [ 1 ] | 2 | | Next >>

Discussion Boards > Active Subjects > Messages as Posted > Electric Forum

Thread 125490 Filter by Poster:
Billy 5 | brokenarrow 1 | greg_g 4 | Iowachild 1 | JD855inWI 1 | kthompson 1 | Peters 1 | steve4300 2 |

 (advanced search)

Picture of the Day
DennisCTB

Food - Kentucky Legend Sliced Ham
Kentucky Legend Sliced Ham


Unanswered Questions

Gas Generator Weather Protecti
Horse Injured Polyrope Electri
Do electric fences keep out de
Any Peruvian Paso Owners Out T
gas powered post driver
My new born foal is really sic
Trailer Axle
dump trailer blueprints


Active Subjects

Gas Generator Weather Protecti
Went to see Dennis Reis this w
Signs to look for prior to lab
leg injury
Broodmare has welts all over h
Some Christmas Humor For Horse
poles in the ground vs. concre
ever thought about moving?


Hot Topics

new app owner
Some Christmas Humor For Horse
Any Peruvian Paso Owners Out T
Heating a Garage
Gas Generator Weather Protecti
Do electric fences keep out de
gas powered post driver
Trailer Axle


Featured Suppliers

Mountain Creek Labradoodles
      MountainCreekLabradoodles.com





New Forums on Gun Sport Shooting and Hunting -- BarrelPoint.com  New Forums on Horses ManePoint.com
Talk Horses at ManePoint
Hunting + Gun Sports at BarrelPoint



Most Viewed

+ Hanging Ceiling Fan in Great room
+ Back-up power
+ need a 110V winch
+ trouble shooting
+ Underground Elec - direct-burial vs in conduit
+ Underground Wiring
+ pole barn sub panel
+ Tapping in to Well Electric
+ Better common light bulbs
+ wiring my new garage

Most Discussion

+ need a 110V winch
+ pole barn sub panel
+ Hanging Ceiling Fan in Great r
+ Back-up power
+ Turn a freezer into a refriger
+ Underground Wiring
+ trouble shooting
+ wiring my new garage
+ Tapping in to Well Electric
+ Electrical Ground Question

Newest Topics

+ LED light bulb hum
+ Breaker Trips After lIghts on 30 minutes
+ Power 120v heat strip off one phase of 240v line
+ Maytag Oven
+ trouble shooting
+ Infrared space heaters
+ T-8 s or T-12 s
+ lighting
+ noalox compound
+ 220 pump shed
















Turbochargers for Tractors and Industrial Machines
Cab Glass for Tractors and Industrial Machines

Alternators for Tractors and Industrial Machines
Radiators for Tractors and Industrial Machines

Driveline Components for Tractors and Industrial Machines
Starter Motors for Tractors and Industrial Machines