 Electrical Ground Question

Again Billy, If this is a secondary panel - that is, if it's deriving power from the same source that supplies other buildings and/or power panels - that new ground bar (electrode) needs to be bonded back to whatever's being used as the common ground. This is typically the ground electrode system associated with the service entrance (electric meter). Not doing so creates unequal ground potential, which in turn still leaves you vulnerable to ground loops, static, et cetera. For electronic equipment, that translates into noise - and electronics don't work their best in noisy electrical environments.

And further to what BA said; if you get the electrician to come back out to do the electrode, he should know enough to bond the new one back to the common ground electrode as part of the job.

//greg//






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 03-05-2006, 11:25 Post: 125585
Billy

TP Contributor

View my Photos

View my Photos  Pics
Join Date: Oct 1999
Location: Southeast Oklahoma
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 975

5
Filter by User
 Electrical Ground Question

Greg, these aren't sub panels. There is a 200 amp main service disconnect right under the electric meter. There's two sets of 3 wires going to each panel in tow different buildings. Below is an email from a friend of mine. This guy knows his shit and deals with high dollar electronics every day.

Billy,

Hey yes...it certainly has been a long time! Where you been! Last I heard you were having problems with your computer and e-mail system. Hope those problems got resolved. Hope everything is going well for you.

Okay now, understanding that you've made a serious investment in equipment to run your houses...then hired someone who claimed to be a trained professional to install this expensive equipment...and understanding that the equipment must be installed properly or it may get destroyed by lightening, power line transients, or any number of other power system anomolies...I would begin by doing the following, and in the same order:

1. Dig a shallow hole about 6' by 3' by 3 feet deep
2. Shoot "electrician" who installed your equipment
3. Dump body in aforementioned hole
4. Lime liberally and then cover with dirt
5. Go back in a couple of days and smooth over the depression from the body shrinking

Now that we have the "electrician" taken care of and out of the way we can get down to correcting what he did.

I assume he ran 220/240 volt AC power to your houses. This would be one leg, another leg, and a neutral line...L1, L2, and N on drawings or diagrams. This being the case your neutral line goes to ground, but only at the distribution transformer. This is as it should be. Don't mess with this.

Leave the neutral and ground bus bars separated.

I don't remember if your houses have concrete or dirt floors in the control equipment rooms. If they're dirt, cool. If they're concrete, I would plan on drilling a hole through it and then filling that in when we're done.

Do you know how far down your water table is? We need to get a ground rod down a couple of feet below the top level of the water table when it's at its lowest. Sometimes this requires an 8 foot rod, sometimes longer. I believe they come in 8, 10, 12, and 16 foot lengths. Let's hope the 8 footer will do and this is the shortest ground rod I would use.

I don't like steel ground rods even if they do meet code. I like solid copper or copper clad rods. Some supply houses will try to sell you a copper plated rod as a clad rod, they're lying to you. Plating is only several micro inches thick, millionths of an inch. A copper "clad" rod will have about a 1/32 to 1/16 inch thick layer of copper around the rod from end to end. If your dirt isn't too bad to dig in and you can use it, I would use solid copper when ever possible.

You need one rod for each control panel.

I would install the rod as close as possible to the control panel. Right below it would be great.

After you're done with this run a cable from the ground bus on the panel to your rod, clamp, and you're good to go. Ground cable - I like to use a braid type cable rather than a solid wire like the power company uses. Solid wire is okay for just a safety wire and low frequency AC, 60 Hz as with line power. One of the more serious issues you have to deal with is lightening, which is a very short duration, high energy content pulse. A ground cable for this is much better when there are many, many more strands of wire in the cable...the more the better. Without getting into the technical details and physics of why, this just presents a much lower impedance (which is a spiffy name for the AC resistance of a conductor) to high frequency energy...lightening. Copper braid isn't cheap, but do we want to protect thousands of dollars worth of controllers with a 10 dollar piece of wire? This is 1/2 inch copper braid. I would use 2 lengths, run in parallel, to ground my panel.

Hope this helps. Let me know if I can be of any further help Billy.


REB

ollar control computer?






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 03-05-2006, 13:14 Post: 125587
greg_g



View my Photos

View my Photos  Pics
Join Date: Jan 2004
Location: Western Kentucky
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 1816

4
Filter by User
 Electrical Ground Question

Oklahoma code notwithstanding, Reb has described to you the way I'd have done it. Following his advice does not require the services of a licensed electrician, because nothing he told you to do breaks the meter seal. At least that's how it works around here. Sounds like a reasonable do-it-yourself fix. Only thing I would add- as before - is to bond all individual electrodes (ground rods) together (and to the common ground) to equalize ground potential.

Curious though - why didn't your electrical inspector catch this?

//greg//






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 03-05-2006, 15:56 Post: 125591
Billy

TP Contributor

View my Photos

View my Photos  Pics
Join Date: Oct 1999
Location: Southeast Oklahoma
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 975

5
Filter by User
 Electrical Ground Question

why didn't your electrical inspector catch this?

Because the electrician and the inspector are the same person and both are idiots. He just happens to work for the company that put all the new equipment in. He's actually a decent electrician but is lazy as hell. I believe the only reason they keep him is he knows how to work on the controllers.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 03-05-2006, 17:31 Post: 125594
Iowachild



Join Date: Mar 2006
Location: Warren, PA
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 1
 Electrical Ground Question

In normal house wiring, the neutral is bonded to the box where the main disconnect is located and a ground conductor runs from the neutral bar to the ground rods. (as in 2 ground rods, 10' apart.) The neutral and ground never come in conatact again. However, when a sub-panel is power in a different building, you can run a three-wire curcuit and bond the nuetral in the sub-panel and run a ground conductor from the neutal bar to ground rods driven at the building where the sub=panel is located. BTW: Never use smaler than #6 copper for a gound conductor. Number * is legal for a 100 amp service, but it requires mechanical protection (conduit), where as #6 does not require protection.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 03-07-2006, 18:19 Post: 125721
steve4300

TP Contributor

Join Date: Dec 2004
Location: NH
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 71

2
Filter by User
 Electrical Ground Question

I personally think he should come out and check it out. Make any repairs at no charge to you. I never tell a custermer how to fix something I did.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
Reply | Pop Up Window Reply | Add PhotoAdd Photo


Page 1 | [ 2 ] |      << Prev

Discussion Boards > Active Subjects > Messages as Posted > Electric Forum

Thread 125490 Filter by Poster:
Billy 5 | brokenarrow 1 | greg_g 4 | Iowachild 1 | JD855inWI 1 | kthompson 1 | Peters 1 | steve4300 2 |

 (advanced search)

Picture of the Day
candoarms

Landscape Maintenance - Elm Tree Removal Minot North Dakota
Elm Tree Removal Minot North Dakota


Unanswered Questions

Gas Generator Weather Protecti
Horse Injured Polyrope Electri
Do electric fences keep out de
Any Peruvian Paso Owners Out T
gas powered post driver
My new born foal is really sic
Trailer Axle
dump trailer blueprints


Active Subjects

Gas Generator Weather Protecti
Went to see Dennis Reis this w
Signs to look for prior to lab
leg injury
Broodmare has welts all over h
Some Christmas Humor For Horse
poles in the ground vs. concre
ever thought about moving?


Hot Topics

new app owner
Some Christmas Humor For Horse
Any Peruvian Paso Owners Out T
Heating a Garage
Gas Generator Weather Protecti
Do electric fences keep out de
gas powered post driver
Trailer Axle


Featured Suppliers

Mountain Creek Labradoodles
      MountainCreekLabradoodles.com





New Forums on Gun Sport Shooting and Hunting -- BarrelPoint.com  New Forums on Horses ManePoint.com
Talk Horses at ManePoint
Hunting + Gun Sports at BarrelPoint



Most Viewed

+ Hanging Ceiling Fan in Great room
+ Back-up power
+ need a 110V winch
+ Underground Elec - direct-burial vs in conduit
+ trouble shooting
+ Underground Wiring
+ Better common light bulbs
+ Tapping in to Well Electric
+ pole barn sub panel
+ wiring my new garage

Most Discussion

+ need a 110V winch
+ pole barn sub panel
+ Hanging Ceiling Fan in Great r
+ Back-up power
+ Turn a freezer into a refriger
+ Underground Wiring
+ trouble shooting
+ wiring my new garage
+ Tapping in to Well Electric
+ Electrical Ground Question

Newest Topics

+ LED light bulb hum
+ Breaker Trips After lIghts on 30 minutes
+ Power 120v heat strip off one phase of 240v line
+ Maytag Oven
+ trouble shooting
+ Infrared space heaters
+ T-8 s or T-12 s
+ lighting
+ noalox compound
+ 220 pump shed
















Turbochargers for Tractors and Industrial Machines
Cab Glass for Tractors and Industrial Machines

Alternators for Tractors and Industrial Machines
Radiators for Tractors and Industrial Machines

Driveline Components for Tractors and Industrial Machines
Starter Motors for Tractors and Industrial Machines