 12-07-2004, 14:37 Post: 101767
Murf



View my Photos

View my Photos  Pics
Join Date: Dec 1999
Location: Toronto Area, Ontario, Canada
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 7054

15
Filter by User
 PTO Generators Observations

Ontario has amongst the tighest electrical safety regulations of any jurisdiction in North America.

Unfortunately we also have a great number of very old electrical services still in operation, and oddly enough our reg.'s don't require that existing services be upgraded.

When that is combined with things like the big ice storm a few years back, the great blackout in the summer of 2003, and the Y2K scare the result is that we have a lot of generators hooked up to painfully out-dated wiring.

I have a neighbour at the cottage who regularly fires up a 25KW diesel genset and feeds it into his KNOB & TUBE wired 100 year old post & beam cottage!!!

Some people are just plain stoooooopid.

Best of luck.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 12-07-2004, 15:51 Post: 101773
denwood



Join Date: Jul 2004
Location: Quarryville PA
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 542

9
Filter by User
 PTO Generators Observations

First let me say that my house is wired correctly for a generator, and not that anyone should do an improper generator hookup, but if you are in a pinch, there is an easy and almost safe way. Make sure you switch off your main 100, 200, or more amp service disconnect first, this protects the power company. Then, just make a double male extention cord that plugs into your generator 240 outlet and also to a 240 welder, compressor, etc. outlet. Make sure the generator output from it's 240 socket is less than or equal to the amp breaker you are back feeding. This lets you choose any circuit in the house to run and isolates you from the power company. It also keeps you from any "rewiring". I use this method at times when I am renovating a house that is not connected to the power company at all.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 12-07-2004, 21:28 Post: 101800
lbrown59

TP Contributor

Join Date: Sep 2004
Location: First Organized Permanent Settlement In The Northwest Territory.
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 931

2
Filter by User
 PTO Generators Observations

Then, just make a double male extention cord that plugs into your generator 240 outlet and also to a 240 welder, compressor, etc. outlet
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
This is dangerous.
No extension cord should have a mail plug on each end.
This is an open invitation to someone getting shocked or electrocuted.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 12-08-2004, 06:34 Post: 101831
kyvette

TP Contributor

View my Photos

View my Photos  Pics
Join Date: Feb 2004
Location: Central Kentucky
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 194

7
Filter by User
 PTO Generators Observations

Denwood, I agree with Ibrown, this is not safe, and you said it yourself "almost safe". There is no middle ground when it comes to safety, its either safe or its not safe. Any installation that fails to meet code, NEC and/or NESC, is considered a dangerous situation.

I would suggest on an existing house panel that is not connected to the utility source that you do the following: remove the main service conductors to the main breaker (typically 200amp) from the panel then connect your generator to the main breaker lugs. This way you will have a visual open connection to the utility and the distribution panel breakers will protect you and the circuit. However, you can overload the generator. A typical house(1500-2500sqft) in our area will use 9 - 13kw. Be sure the connecting conductors between the generator and panel are rated to carry the load. Better still, get advice from your electrical inspectors. Dave






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 12-08-2004, 07:57 Post: 101839
Murf



View my Photos

View my Photos  Pics
Join Date: Dec 1999
Location: Toronto Area, Ontario, Canada
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 7054

15
Filter by User
 PTO Generators Observations

Dave is right. Denwoods method could likely kill an unsuspecting linesman who failed to carefully check all three conductors assuming the lines were safe.

In fact this is EXACTLY the methgod used by my neighbour that led to his electrical service being disconnected by the utility.

In almost all cases the "mains" in a house are only double pole single throw switches, this means only the two "hot" wires are disconnected, this leaves the neutral side and the ground bonded through to the incoming lines. They are the potential problem.

If under these circumstances you had a faulty wire somewhere you could, using the ground and neutral conductors electrify the lines in front of your house.

This is what electrocutes linesmen working on "dead" lines.

The other hazard is merely burniung down the house or wrecking some expensive electronic equipment. Since you are tapping into the 220v. side of the wiring and depending on luck to have a balnced split between the two legs of the 220 wiring you run the risk of having all (or even most) of the load on one side of the generator. This could lead to very low voltages and much higher than normal current flowing.

The ONLY safe way to use a generator is to either plug the desired item directly into the genset, or have a proper transfer panel, a switch which will COMPLETELY isolate the generator and all the load to be transferred to it from the incoming utility lines.

Best of luck.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 12-08-2004, 17:20 Post: 101903
denwood



Join Date: Jul 2004
Location: Quarryville PA
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 542

9
Filter by User
 PTO Generators Observations

I am aware and agree with all your posts. Safety is of great importance, unfortunatly it is the first thing most people are willing to compromise on. Just look at the speed limit and the speed poeple actually drive. Even hooking the generator directly to the main lugs is having a double male cord, male at one end bare wires at the other. Putting your self at risk is one thing, putting others at risk is where the line needs to be drawn. Certainly a person should have a good grasp of what they are doing and the risks involved to remain safe. You know what they say "Common sense isn't"






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 01-16-2005, 20:38 Post: 104349
steve4300

TP Contributor

Join Date: Dec 2004
Location: NH
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 71

4
Filter by User
 PTO Generators Observations

As a eletrical contractor I Have to say Never back feed a house, it can kill. The transformer out on the street works both ways if it reduces the voltage for your house it can increase the voltage from you generator. Now there are a lot of good tranfer switches out there for all sizes of generators. they will disconnect the two hot leads for the circuits you want on the generator. I have never seen a disconect that also disconnects the neutral or ground wires. Here is agood link for small generator transfers.






Link:   pro/trans - reliance controls 

Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 01-25-2005, 12:54 Post: 104894
denwood



Join Date: Jul 2004
Location: Quarryville PA
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 542

9
Filter by User
 PTO Generators Observations

Steve4300, you are right about the transfer switches being 2 pole, so the grounds are always still connected to the utility wires. Mine is a midwest installed by a licensed electrician and inspected and to code. So if these are ever a problem, it is really a code problem. Before you think Murf is a dummy or just likes to type, remember he is from Canada and it may be different there, as many things are. Heck they even had the flu shot and we couldn't get any. As far as overloading one side of the generator? Doesn't every single person who hooks a 220 generator to a breaker panel, in any manner, that also uses 120 circuits, pose a slight risk of that? When you energize a breaker box with 220, you energize both poles which alternate breakers as you go down each column. If by chance it happens that every other 120 breaker is used at the same time, it could load one side. Other than proper planning of breaker placement, is there any other way to reduce this slim possibility?






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 01-25-2005, 20:37 Post: 104923
steve4300

TP Contributor

Join Date: Dec 2004
Location: NH
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 71

4
Filter by User
 PTO Generators Observations

denwood , I do believe electrical codes are stricter in Canada. As far as balancing the loads on a generator, most electricians use a clamp -on amp meter and try to figure out what each load is drawing.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 01-26-2005, 07:49 Post: 104942
Murf



View my Photos

View my Photos  Pics
Join Date: Dec 1999
Location: Toronto Area, Ontario, Canada
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 7054

15
Filter by User
 PTO Generators Observations

You are both correct, the electrical safety reg.'s in Canada are amongst the strictest in the world.

Here we must have a transfer switch which a) breaks the neutral bond between the generator supply and the utility's supply lines, and b) it must be of a "break-before-make" design, in other words it must open all 3 circuits from the utility's lines BEFORE it can connect to the generator. They also MUST be capable of transferring their full rated capacity UNDER LOAD.

The ground wire is a moot point since one conductor cannot form a circuit, especially when it's grounded anyway.

Most transfer switches here are also equipped with a neutral bond break delay to ensure there is no out of phase issues created by the transfer switch.

IMHO, a 2 pole transfer switch is just a big poke waiting to happen to someone, likely an unsuspecting linesman.

Best of luck.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
Reply | Pop Up Window Reply | Add PhotoAdd Photo


Page 1 | 2 | 3 | [ 4 ] | 5 | 6 | 7 | 8 | 9 |      << Prev | Next >>

Discussion Boards > Active Subjects > Messages as Posted > Generators Forum

Thread 72825 Filter by Poster:
AnnBrush 10 | Art White 2 | Billy 1 | bud4410 1 | Chief 2 | denwood 9 | DRankin 6 | grinder 2 | harvey 11 | HuckMeat 1 | jdlx173 1 | kyvette 7 | lbrown59 2 | Murf 15 | ncrunch32 6 | NHDaveD 2 | steve4300 4 | TomG 3 |

 (advanced search)

Picture of the Day
joyce1

Just For Fun Off Topic - Too much Snow Too Soon for me
Too much Snow Too Soon for me


Unanswered Questions

Gas Generator Weather Protecti
Horse Injured Polyrope Electri
Do electric fences keep out de
Any Peruvian Paso Owners Out T
gas powered post driver
My new born foal is really sic
Trailer Axle
dump trailer blueprints


Active Subjects

Gas Generator Weather Protecti
Went to see Dennis Reis this w
Signs to look for prior to lab
leg injury
Broodmare has welts all over h
Some Christmas Humor For Horse
poles in the ground vs. concre
ever thought about moving?


Hot Topics

new app owner
Some Christmas Humor For Horse
Any Peruvian Paso Owners Out T
Heating a Garage
Gas Generator Weather Protecti
Do electric fences keep out de
gas powered post driver
Trailer Axle


Featured Suppliers

Mountain Creek Labradoodles
      MountainCreekLabradoodles.com





New Forums on Gun Sport Shooting and Hunting -- BarrelPoint.com  New Forums on Horses ManePoint.com
Talk Horses at ManePoint
Hunting + Gun Sports at BarrelPoint



Most Viewed

+ 3 Pt PTO generators
+ Generator set up ideas wanted
+ PTO Generators Observations
+ PTO driven vs Gas engine
+ Best Portable Generator 7500W Review
+ PTO Horsepower and Generator Question
+ I love my Generator
+ Features to look for in stand alone generator
+ building budget auto-backup system
+ Yamaha Generator problem

Most Discussion

+ Generator set up ideas wanted
+ PTO Generators Observations
+ 3 Pt PTO generators
+ PTO Horsepower and Generator Q
+ I love my Generator
+ Features to look for in stand
+ Yamaha Generator problem
+ Best Portable Generator 7500W
+ Power stability with PTO gener
+ Measuring Frequency in a gener

Newest Topics

+ no electric power
+ Premium Fuel for Generator Avoid Ethanol Myth
+ How to increase Portable Generator Wattage output
+ Gillette vs Winco Generator Review
+ Best Portable Generator Temporary Shelter
+ Portable Generator House Backup Grounding
+ Dielectric antioxidant grease
+ Welder generator burning up tool switches
+ Welder generator burning up tool switches
+ PowerBoss Brush versus brushless Generators
















Turbochargers for Tractors and Industrial Machines
Cab Glass for Tractors and Industrial Machines

Alternators for Tractors and Industrial Machines
Radiators for Tractors and Industrial Machines

Driveline Components for Tractors and Industrial Machines
Starter Motors for Tractors and Industrial Machines