 PTO Generators Observations

I got my new Tiger Power generator from Dyna Tech in PA. It is a 20 KW generator. However the 20's were out of stock so they asked if a 30kw would be ok for a subisitute, same money. Uhhhhhhhhhh geezeeeeeee I think it would be ok. Remembering what Art said about to much tractor and not enough generator.

I have HP enough for about 17KW so the 20 was just over the safety line.

Anyway finially got trailer built photo # 7 and tested generator. All breakers off and service disconnected PTO gen to operating speed Volts at 220 and 60kh cycle it came in at 100 rpm less the rated 540 rpm.

Turning everything on in the house did not even phase it. The tractor eng never grunted as the small loads were applied. The tractor did grunt a little and voltage never quivered when the 220 water pump kicked on. I did not try and see if my air compressor or other large stuff would affect it because they would not be used anyway.

I had the gen out the other day and plugged my welder into it and even at the heaviest amp setting and biggest rod I have the tractor only made a very small grunt as arc was struck.

I am a happy camper with this set up. But do think I'll look for a small gen to run wood stove fans at night.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 01-01-2004, 07:17 Post: 72827
Billy

TP Contributor

View my Photos

View my Photos  Pics
Join Date: Oct 1999
Location: Southeast Oklahoma
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 975
 PTO Generators Observations

Sounds like a heck of a deal.

On the small gen for the heater fan. The guys that put my generator in (pic #1) had a dandy little generator. It was small enough to carry around with one hand.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 01-01-2004, 10:26 Post: 72833
DRankin



View my Photos

View my Photos  Pics
Join Date: Jan 2000
Location: Northern Nevada
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 5105

6
Filter by User
 PTO Generators Observations

Harvey, clear up a couple of points if you please.

Did you actually get a 30 KW?

And run through the RPM thing again? Is your PTO shaft turning 100 rpm less or your engine running 100 under the rated pto speed?

Thanks.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 01-01-2004, 11:35 Post: 72840
TomG

TP Contributor

Join Date: Feb 2002
Location: Upper Ottawa Valley
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 5406

3
Filter by User
 PTO Generators Observations

Sounds like a good present and good it's working beyond expectations. I think what you are experiencing is that ratings for AC equipment are pretty conservative and houses usually are running much below the service rating.

Even fairly high starting surges for electric motors are of short duration. There's a decent change that inertia of the engine, drive train and larger generator is sustaining the rpm for the short time it takes for a motor to come up speed even if the requirements are greater than the tractor's pto hp. A larger generator and higher surges will be a bit harder on the pto clutch. You probably don't have to consider if the generator is exceeding it's duty cycle though.

Several motors starting up at the same time could be a different story though. I know that's what my 6.5kw standalone doesn't like much--never have popped a main though. It is possible for a big generator to bring a tractor down. That might be an issue if a number of large motors are on the system and it's running unattended. If it's an issue smaller mains probably could be installed.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 01-01-2004, 12:05 Post: 72844
harvey



View my Photos

View my Photos  Pics
Join Date: Sep 2000
Location: Moravia, NY
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 1534

11
Filter by User
 PTO Generators Observations

Mark yes it's a 30kw gen. 125 main breaker, however the labels read 20 kw because it's what I paid for. I have no issue with that I am pleased with the heavier setup. These folks treated me very good and I appreciate the no cost upgrade. It was only a couple of weeks from time of order till it was at home.

I'd have to look for sure but me thinks my tractor is rated at 2700 for 540 pto? the generator runs at 2600 or 100 rpm below whatever it is rated on the tach.

Tom you are right about the surges with bigger motors. Many times when the milk cooler compressor kicked in it really would make a 100hp tractor grunt, of course big vacum pump running at same time. We won't even discuss silo unloaders. I'm glad most of those are a thing of the past. As I said everything run very smooth with no noticiable fluxuations in the voltage meters. Of course that is why I'm happier with more generator than tractor. A big tractor would melt down a small generator and a big generator will bring a small tractor to its knees with a brown out and no damage done.

Thats why I did not try any of my larger shop tools. I guess I could just to see.

The main purpose of generator is: the boss to keep her shop running along with the computers when she is working, lighting and if I wanna watch TV in the evening. Generally just making things more comfortable for us.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 01-01-2004, 16:19 Post: 72848
Art White



View my Photos

View my Photos  Pics
Join Date: Jan 2000
Location: Waterville New York
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 6854

2
Filter by User
 PTO Generators Observations

With a spare gas tank around you have the Farmall M for back-up if ever the need. That way the loader tractor would be available for normal details. Nice work Harvey!






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 01-01-2004, 19:02 Post: 72859
harvey



View my Photos

View my Photos  Pics
Join Date: Sep 2000
Location: Moravia, NY
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 1534

11
Filter by User
 PTO Generators Observations

Art you must read minds!






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 01-01-2004, 20:13 Post: 72862
Art White



View my Photos

View my Photos  Pics
Join Date: Jan 2000
Location: Waterville New York
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 6854

2
Filter by User
 PTO Generators Observations

Good luck with it as it seems like you do have it beat!






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 01-02-2004, 06:51 Post: 72883
TomG

TP Contributor

Join Date: Feb 2002
Location: Upper Ottawa Valley
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 5406

3
Filter by User
 PTO Generators Observations

Good to hear a happy man! The issue of big tractors with small generators may be an issue for people still looking but not for Harvey. I think most melt downs come from people running a generator between its continuous and peak ratings for times longer than the duty cycle rating. That can easily happen with small lower-end generators. The may be advertised to impress by low cost and high peak ratings but at the expense of shorter duty cycles. The generator's breakers protect against peak loads but not against prolonged loads between the continuous and peak ratings. To manage this problem, the generator has to be larger than typical continuous loads. Harvey isn't likely to have this issue but I do. The automatic start up panel discussed here awhile back that shuts down circuits on a priority basis to manage load is a potential fix.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 01-03-2004, 08:57 Post: 72947
grinder

TP Contributor

View my Photos

View my Photos  Pics
Join Date: Oct 2003
Location: central Maine
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 677

2
Filter by User
 PTO Generators Observations

http://www.gov.on.ca/OMAFRA/english/engineer/facts/00-059.htm

Harvey
I am thinking of getting a gen. for my 7500.
Can I use this info from Canada?






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
Reply | Pop Up Window Reply | Add PhotoAdd Photo


Page [ 1 ] | 2 | 3 | 4 | 5 | 6 | 7 | 8 | 9 | | Next >>

Discussion Boards > Active Subjects > Messages as Posted > Generators Forum

Thread 72825 Filter by Poster:
AnnBrush 10 | Art White 2 | Billy 1 | bud4410 1 | Chief 2 | denwood 9 | DRankin 6 | grinder 2 | harvey 11 | HuckMeat 1 | jdlx173 1 | kyvette 7 | lbrown59 2 | Murf 15 | ncrunch32 6 | NHDaveD 2 | steve4300 4 | TomG 3 |

 (advanced search)

Picture of the Day
candoarms

Landscape Maintenance - Elm Tree Removal Minot North Dakota
Elm Tree Removal Minot North Dakota


Unanswered Questions

Gas Generator Weather Protecti
Horse Injured Polyrope Electri
Do electric fences keep out de
Any Peruvian Paso Owners Out T
gas powered post driver
My new born foal is really sic
Trailer Axle
dump trailer blueprints


Active Subjects

Gas Generator Weather Protecti
Went to see Dennis Reis this w
Signs to look for prior to lab
leg injury
Broodmare has welts all over h
Some Christmas Humor For Horse
poles in the ground vs. concre
ever thought about moving?


Hot Topics

new app owner
Some Christmas Humor For Horse
Any Peruvian Paso Owners Out T
Heating a Garage
Gas Generator Weather Protecti
Do electric fences keep out de
gas powered post driver
Trailer Axle


Featured Suppliers

Mountain Creek Labradoodles
      MountainCreekLabradoodles.com





New Forums on Gun Sport Shooting and Hunting -- BarrelPoint.com  New Forums on Horses ManePoint.com
Talk Horses at ManePoint
Hunting + Gun Sports at BarrelPoint



Most Viewed

+ 3 Pt PTO generators
+ Generator set up ideas wanted
+ PTO Generators Observations
+ PTO driven vs Gas engine
+ Best Portable Generator 7500W Review
+ PTO Horsepower and Generator Question
+ Features to look for in stand alone generator
+ I love my Generator
+ building budget auto-backup system
+ Yamaha Generator problem

Most Discussion

+ Generator set up ideas wanted
+ PTO Generators Observations
+ 3 Pt PTO generators
+ PTO Horsepower and Generator Q
+ I love my Generator
+ Features to look for in stand
+ Yamaha Generator problem
+ Best Portable Generator 7500W
+ Power stability with PTO gener
+ Measuring Frequency in a gener

Newest Topics

+ no electric power
+ Premium Fuel for Generator Avoid Ethanol Myth
+ How to increase Portable Generator Wattage output
+ Gillette vs Winco Generator Review
+ Best Portable Generator Temporary Shelter
+ Portable Generator House Backup Grounding
+ Dielectric antioxidant grease
+ Welder generator burning up tool switches
+ Welder generator burning up tool switches
+ PowerBoss Brush versus brushless Generators
















Turbochargers for Tractors and Industrial Machines
Cab Glass for Tractors and Industrial Machines

Alternators for Tractors and Industrial Machines
Radiators for Tractors and Industrial Machines

Driveline Components for Tractors and Industrial Machines
Starter Motors for Tractors and Industrial Machines