 03-28-2004, 18:21 Post: 81423
brokenarrow



Join Date: Jan 2004
Location: Wisconsin
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 1288

2
Filter by User
 wiring my new garage

Ok, I just read all thru the post, "wiring a old barn" or what ever it was. I have a few questions that may over lap and a few new also. My new Garage is around 200' from my house electric. In my house I have an on demand hot water system (for now) very happy with it for this is my second home and when we arive its usually really late and showers can be took by everyone (5 of us) without waiting for heating the water. anyway, This has a 70 amp system (dont use all of it all the time but will flicker the lights a bit. Laughing out loud. I need to get electric to my garage, and the post talking about asking the electric co-op what to do is probably the best. Wondering if I can have the electric company run anouther secondary main (from the box which lowers the juice from the main) to my garage and have it on the same bill without anouther mandatory user fee? (17 bucks a month) ouch. I dont know what I will need for power in the future since I am moving there in 4 -5 years and I am a tool and die maker which means I will more than likely have machines out there. The power company charges $3.75 a foot for the burial and the wire (I think its a deal) although I can put it in for less just how much is my time worth????? I did just buy a new tractor and it may be more fun than not, but I still can find other things that are better (or more fun) that need to be done with it. That 250' extension wire is starting to get old (wrapping it up everytime I am done with it) Laughing out loud>






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 03-28-2004, 19:06 Post: 81426
Peters

TP Contributor

View my Photos

View my Photos  Pics
Join Date: Feb 2002
Location: Northern AL
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 3034

2
Filter by User
 wiring my new garage

Questions:
What amp service do you have into the house now?
Is there any 3 phase equipment that you need in the barn?
How many amps do you anticipate needing in the barn?
Peters






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 03-28-2004, 20:38 Post: 81432
loghouse95



Join Date: Jul 2003
Location: missouri
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 87

2
Filter by User
 wiring my new garage

My shop is about 150 ft from my meter, I wired my shop and run the appropriate size electrical cable from my breaker box to the meter, leaving about 8 ft of cable out of the ground to wire to the main meter. I had previously contacted the electrical co-op and explained to them what I was doing, They told me to leave the last few feet of trench uncovered so they could confirm I was burying the cable the correct depth, I installed the cable in conduict.when I was ready for them to connect me they came out and hooked everything up at no charge I recommend you wire your shop with a 200 amp box so you will have enough power to run all your "TOYS" Good Luck






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 03-28-2004, 21:00 Post: 81436
TomG

TP Contributor

Join Date: Feb 2002
Location: Upper Ottawa Valley
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 5406

6
Filter by User
 wiring my new garage

I think there are splitters that can be installed after a meter. Ordinarily they won't work because most times an existing service panel and service line have the same rating. A new heavier service line can be expensive but maybe not as expensive as two separate services.

An alternative depending on how full the house panel is might be running a branch circuit off the house panel to a sub-panel in the garage. Branch circuits most places can be up to 125A and service panels can be 'over-fused' to 110% of rating or so. At 200' at least one step over-sized wire would be required. There would be details to check. I suppose that in very stringent code areas it might be possible that a 200' run might require wire size that wouldn't be approved for the size breaker needed. Unlikely but possible and you don't want to be committed to something only to find that it can't be approved.

I did the service at out camp as a branch circuit off a main panel. New 200A service to a pole panel and a 100A branch circuit underground to the 100A panel in our 40' construction trailer. $3.75 a foot sounds like a real deal. If it's 100A copper direct burial wire I doubt I could buy the wire for that price. Trenching is fun though.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 03-28-2004, 21:49 Post: 81439
brokenarrow



Join Date: Jan 2004
Location: Wisconsin
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 1288

2
Filter by User
 wiring my new garage

Thanks all of you
Tom
I actually paid $3.25- 4 years ago to go 435 feet from the poles under ground to my house in the woods.

Do most electric meters have a spot on them to connect anouther line (say one to go to my garage?)

Here is a spin of one of the other posts on a different thread here. We have NO inspection and NO zoning so basically there is NO code ( that is scary huh?) Anyway I had the whole house wired up and ready for the electric to be put into my box. I had a buddy (electricion for 18 years) check my work and he approved. The electric service guys came out and ran the wires. They asked me if I wanted to hook the wires up before they connected it to the box outside. I told them I would but did not have and tools to do it with at that time (or atleast the allen wrenches needed) He told me, "dont worry I aint supposed to do this but what the heck" He hooked it up and tightened everything up. 3 weekd latter (on a SUNDAY) I was putting in 2 more lines in the box and I noticed the main line moving!!!! The allen screw backed off and was letting this bent heavy duty live wire pull back. It was almost out and I though the tension on it would (if it pulled out snap back and touch the whole system) I freaked!!! I called the co-op and they told me if I wanted I could break the seal and pull the meter! Phewww Job solved and I am still hear to talk about it. Moral of the story????? Never let a trained person do a job for you that you know you would do as good or better.
I tend to ask alot of questions, do alot of homework, and bring someone in that knows what he is doing to check my work (if I never done something before) I know I wont do something that is questionable so I am better off doing it myself most of the time (especially where my other house is located)
Hey thanks for the ideas, I will talk with the co-op next week and get their opinion also.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 03-29-2004, 06:00 Post: 81456
TomG

TP Contributor

Join Date: Feb 2002
Location: Upper Ottawa Valley
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 5406

6
Filter by User
 wiring my new garage

I've never seen a meter base that could split a service line but that doesn't mean they don't exist. I think the main issues you'll face is that the total of rating service panel or panels connected to a service can't (or in your case shouldn't) exceed the rating of the service line. In addition, splitting the line behind the meter would require the garage feed to be treated as a service line. Codes for service lines are more stringent than for branch circuits. If your service panel already equals the line rating, then you're sort of stuck.

Codes are pretty conservative but they're designed so life expectancy of wiring is around 50 years. Higher than rated loads make wiring run hotter, which shortens the expected life. If you're 'code free' then you can make a decision to exceed ratings and shorten service life but it's good to recognize the risks and boy have I seen people taking huge risks. Your experience with the line and lug is also why lines can't be ganged onto the terminal lugs. Also for that reason I tighten the lugs in several stages separated by several days before going live.

Irrespective of co-op arrangements and lack of inspections, codes are basically good sense and intended to keep houses from burning down etc. Working to code is pretty good practice even if it isn't required. Many retail and wholesale suppliers have 'Electrical Codes Simplified ' books that are pretty good for keeping an amateur (and I'm one) pretty close to codes. The books give quite a bit of detail about trenching requirements for underground feeds and for load planning.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 03-29-2004, 06:41 Post: 81459
hardwood

TP Contributor

Join Date: Dec 2002
Location: iowa
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 3582
 wiring my new garage

My only comment comes from experience, I am not any kind of an electrician, so I let the pros do that. I've rewired the main shop three times since it was built (1981). The last time was three phase and I think 440 volts, I don't have a clue how many amps, but some of those breaker boxes are big. The local REC was very helpfull in planning things to meet code, etc. Another lesson learned from experience, whenever you bury a line run it thru an underground conduit that's at least twice as big as you need now, I'll guarantee someday you'll need heavier wires and doing that now makes upgrades a simple matter. hope this helps, Frank.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 03-29-2004, 07:35 Post: 81462
Peters

TP Contributor

View my Photos

View my Photos  Pics
Join Date: Feb 2002
Location: Northern AL
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 3034

2
Filter by User
 wiring my new garage

Like you I also wired the house my self and had a electricial inspect. I asked the questions as there are a number of ways of doing it.
I have one barn off a 100 amp breaker in the house. I put in a large 300 amp service and then break off a separate 100 amp leg to another box in the barn. If you are not running a heat pump or some thing this is plenty of energy.
The new meter base I put in on the house has lugs for an additional leg out of it , after the meter. I am sure you could just change the meter base.
I also have another barn on a separate 200 amp service, but have a hot water heater, pool pump and spa on that service.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 03-29-2004, 12:07 Post: 81477
loghouse95



Join Date: Jul 2003
Location: missouri
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 87

2
Filter by User
 wiring my new garage

I have two additional 220 volt lines (my shop and and guest house) run from my meter that the electrical co-op hooked up for me.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 03-30-2004, 06:03 Post: 81527
TomG

TP Contributor

Join Date: Feb 2002
Location: Upper Ottawa Valley
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 5406

6
Filter by User
 wiring my new garage

In most places the utility is responsible for making connections to service panels. If they connect it then it's got be up to code so there's no debate there. I'm assuming that meter bases with additional lugs are larger than the standard jumbo bases because I can't imagine for example that there'd be enough room in a 200A jumbo base for three 100A lines in addition to 6 200A lines required for standard 200A service. I don't know if the additional lugs Peters mentioned would accommodate heavy service line not.

I'm reasonably certain the idea wouldn't fly here, although the last service I installed was going on 4 years ago now. It might be a good deal if the idea flies but to me splitting still is equivalent a branch circuit in terms of total load rating on the utility line and a branch circuit hookup should be easier. I really can't imagine that existing service line would be so above a service panel load rating that an additional 100A could be hung on it but who knows? Similarly I can't imagine a utility being too happy about residential service with multiple disconnects but again maybe it's a good deal if the idea flies. Our utility is conservative and the rules worked to are pretty restrictive.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
Reply | Pop Up Window Reply | Add PhotoAdd Photo


Page [ 1 ] | 2 | | Next >>

Discussion Boards > Active Subjects > Messages as Posted > Electric Forum

Thread 81423 Filter by Poster:
brokenarrow 2 | hardwood 1 | kully560 2 | kwschumm 1 | loghouse95 2 | Peters 2 | stan1234 2 | texbaylea 1 | TomG 6 |

 (advanced search)

Picture of the Day
candoarms

Landscape Maintenance - Elm Tree Removal Minot North Dakota
Elm Tree Removal Minot North Dakota


Unanswered Questions

Gas Generator Weather Protecti
Horse Injured Polyrope Electri
Do electric fences keep out de
Any Peruvian Paso Owners Out T
gas powered post driver
My new born foal is really sic
Trailer Axle
dump trailer blueprints


Active Subjects

Gas Generator Weather Protecti
Went to see Dennis Reis this w
Signs to look for prior to lab
leg injury
Broodmare has welts all over h
Some Christmas Humor For Horse
poles in the ground vs. concre
ever thought about moving?


Hot Topics

new app owner
Some Christmas Humor For Horse
Any Peruvian Paso Owners Out T
Heating a Garage
Gas Generator Weather Protecti
Do electric fences keep out de
gas powered post driver
Trailer Axle


Featured Suppliers

Mountain Creek Labradoodles
      MountainCreekLabradoodles.com





New Forums on Gun Sport Shooting and Hunting -- BarrelPoint.com  New Forums on Horses ManePoint.com
Talk Horses at ManePoint
Hunting + Gun Sports at BarrelPoint



Most Viewed

+ Hanging Ceiling Fan in Great room
+ Back-up power
+ need a 110V winch
+ trouble shooting
+ Underground Elec - direct-burial vs in conduit
+ Underground Wiring
+ pole barn sub panel
+ Tapping in to Well Electric
+ Better common light bulbs
+ wiring my new garage

Most Discussion

+ need a 110V winch
+ pole barn sub panel
+ Hanging Ceiling Fan in Great r
+ Back-up power
+ Turn a freezer into a refriger
+ Underground Wiring
+ trouble shooting
+ wiring my new garage
+ Tapping in to Well Electric
+ Electrical Ground Question

Newest Topics

+ LED light bulb hum
+ Breaker Trips After lIghts on 30 minutes
+ Power 120v heat strip off one phase of 240v line
+ Maytag Oven
+ trouble shooting
+ Infrared space heaters
+ T-8 s or T-12 s
+ lighting
+ noalox compound
+ 220 pump shed
















Turbochargers for Tractors and Industrial Machines
Cab Glass for Tractors and Industrial Machines

Alternators for Tractors and Industrial Machines
Radiators for Tractors and Industrial Machines

Driveline Components for Tractors and Industrial Machines
Starter Motors for Tractors and Industrial Machines